Results 1 to 7 of 7
Thread: Pull and Junction Box Sizing
  1. #1
    Join Date
    Mar 2003
    New York
    Posts
    29
    314.28 gives requirement for the LxW dimensions for Pull / Juction Boxes.
    Are there requirements for minimum volume ?
    314.16 does address this but only up to #6 conductors.
    Am I missing something?
  2. #2
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    Re: Pull and Junction Box Sizing
    As long as you meet the requirements specified in 314.28, volume calculations do not need to be made. This is figured into the respective formulas.
    Table 314.16(A) does not go above #6 because you wouldn't be able to put anything larger than #6 in the particular boxes listed. If you are installing larger than #6 conductors, you will have to perform a box fill calcualtion and select a box with the minimum volume allowance.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  3. #3
    Join Date
    Mar 2003
    New York
    Posts
    29
    bph...
    Thanks for the reply, but I guess that is what I am asking ... how to perform box fill calculations for conductors over #6, say 250's.
    Thanks again for the help.
  4. #4
    Join Date
    May 2003
    Salt Lake City, Utah
    Posts
    5,319
    I would think that bending radius would become an issue before box fill would when dealing with 250's.
    Ryan Jackson, Salt Lake City
    Inspector, Instructor
  5. #5
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    Box fill calculations are really designed for boxes that are intended to be used as an outlet where a device or fixture will be mounted.
    There are simply not many applications that would require larger than #6 branch-circuits that terminate into a box.
    Above #6 are generally feeders and service conductors that may require pull boxes, j-boxes, and conduit bodies, but will terminate in large enclosures like panelboards and cabinets.
    However, you may be able to determine a ratio using 314.16 to determine larger sized conductors. I have never run into this problem or had a need to do so.
  6. #6
    Join Date
    Jul 2003
    Posts
    1
    The Box Dimesionning is what you have to consider, allowing at all time the space for the bending radius of the conductor, The rule says that for straight pull Box Size should be At least 8 Times the Conduit Size, for Perpendicular Pull The Diagonal Dimension fron Conduit Center To Conduit Center is 6.5 Times Conduit Size, The Depth Of The Box Should Be Twice the size the largest conduit entering the box. Conduit Spacing One Conduit Size OC.