Can I hang data cable across parking lot poles

Status
Not open for further replies.

harrisvt

Member
I have steel parking lot poles and I want to hang low voltage data cable across the poles up about 35 feet in the air. The poles have 480V power that rises up inside the poles. They came with a sticker that said they were not to be used to suspend any other kind of cabling. Is there an NEC rule against this?
Thanks.
 

harrisvt

Member
Yes, but did I really?

Yes, but did I really?

Though it looks to be a no-no, is there an NEC code that would prevent it.?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
harrisvt said:
They came with a sticker that said they were not to be used to suspend any other kind of cabling.
110.3(B)

Installation and Use Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
Roger
 