Consultant

Status
Not open for further replies.

camaelec

Member
I have a project that falls under the NEC 2002. The project inspector is stating that underground concrete pullboxes with metal covers need to have the covers grounded per 314.28(C). 314.28(C) refers me to 250.110 which states "....fixed equipment LIKELY to become energized...". My opinion is that the pullbox cover is not "likely" to become energized as the splices are insulated and sealed with resin kits of the like.

Any suggestions?

Thanks.
 
Last edited:

jrannis

Senior Member
We bond metallic pullbox covers, maybe due to a couple of electrocutions a few years back.
Ive seen some real bad work in underground junction boxes. I tend to agree with your inspector
 

wirenut1980

Senior Member
Location
Plainfield, IN
I guess my response would be that nobody knows how likely it is that the cover might become energized. But given all the press on contact voltage deaths and injuries, I would definately bond the metal cover.
 

jdsmith

Senior Member
Location
Ohio
Stonewall said:
I would bond the covers to the EGC. If over 1000V, I would also locally ground.

Why locally ground? Shouldn't the EGC provide the lowest impedance path back to the breaker?
 