Page 1 of 2 12 LastLast
Results 1 to 10 of 15
Thread: DC to AC power conversion formula
  1. #1
    Join Date
    Jun 2003
    Maryland
    Posts
    82
    I need to calculate the AC power required to serve telecommunications equipment. The data I have on the equipment is given with its DC value (i.e. 40A at -48VDC). How can I convert this DC load to AC (say 240VAC single phase)?
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,939
    Re: DC to AC power conversion formula
    If you are asking what amount of AC power is the same as the DC you have described, then that is simple. Power is power. 40 amps times 48 volts (we can safely ignore the negative sign) equals 1920 watts. Now divide that by 240 VAC and you get 8 amps. But I think that what you really need to know is what type of power converter you need to accomplish your desired conversion. I can't help you with that, as electronics and I do not get alone.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Jun 2003
    Maryland
    Posts
    82
    Actually, your first response was the one I was looking for. I've seen the formula AC=DC/.636 tossed around--Is this perhaps used for equating AC and DC voltages (not power)?
  4. #4
    Join Date
    Feb 2003
    Fl
    Posts
    17,087
    120v AC / .707 = DC. In otherwords 170v AC (Peak Value) is the equivalent of 120 v DC.
    Is that what you were asking?
    edited to clarify my wording
    Roger
    [ August 10, 2005, 11:29 AM: Message edited by: roger ]
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,939
    I tried to play around with the "0.636" number, without success. I can't figure out its origin. It does not appear to help in the conversion of DC power to AC power, for any of the commonly used voltage levels (12 VDC, 24 VDC, 48 VDC, 120 VAC, 208 VAC,240 VAC, etc.).
  6. #6
    Join Date
    Jun 2003
    Posts
    6,883
    0.636 is the average value of a sine wave.
    0.707 is the RMS value of a sine wave.
    Steve
  7. #7
    Join Date
    Jun 2003
    Posts
    6,883
    My mistake, .636 is the average value of a "rectified" sine wave. The average of a sine wave would be zero, since the negative half equals the positive half.
    Steve
  8. #8
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,939
    I did notice earlier that 0.636 was approximately equal to 2 divided by pi. I didn't think it was worth mentioning. But based on steve66's statement, I just did the integration, and confirmed that the average value of a rectified sine wave is 2/pi. But I still don't see how anyone would say that to convert DC power to AC power, you divide by that number. I think the "rule of thumb" that msteiner had been told is nonsense.
  9. #9
    Join Date
    Nov 2004
    Posts
    3,172
    Reading between the lines, the question seems to be, "How much alternating current at 240V is required to operate a 40A, 48Vdc telephone power supply?"
    If that is the case and assuming 75% efficiency,
    Irms = 40Adc x 48Vdc/(240Vrms x 0.75) = 11A
    Sounds like a 20A, 240V circuit to me.
    One would have to see the specs on the equipment to be absolutely sure though.
    Oops, had to correct some typos.
    [ August 10, 2005, 05:26 PM: Message edited by: rattus ]
    Don't mess with B+!
    (Signal Corps. Motto)
  10. #10
    Join Date
    Jun 2003
    Maryland
    Posts
    82
    The last post by rattus is essentially what I was looking for--thanks for the reminder to incorporate efficiency.