This is sort of simple but i need another opinion. If im sizing service cables for a single phase, 200 amp 3-wire panel, 120/240 i have 100 amps on each leg max right? so I can size cable to be a 3awg? As opposed to a 200 amp 3 phase 4 wire 208y/120 panel with 200 amp on each leg. which would need 3/0 service conductors? Just a general question so im not looking at distance of run, cable type etc.
Thanks
Ron
Thanks
Ron