Page 2 of 2 FirstFirst 12
Results 11 to 16 of 16
Thread: Adjustment Factors for Conductors with Load Diversity
  1. #11
    Join Date
    Jun 2003
    Posts
    6,828
    Re: Adjustment Factors for Conductors with Load Diversity
    With all those luxuries, you must work in the marketing dept. Charlie!! I remember a paticular "Dilbert" cartoon strip had a doorway with a sign over it that read "Marketing Department - Two Drink Minimum"
    The thing that bugs me is that I only have to provide 1VA per square foot. So I design all the conduits and everything so I don't have to derate the wire. Now, if I add more circuits (maybe just because I don't want Charlie's heater to trip the breaker to George's computer), I may be forcing myself to also use larger wire.
    I guess I just don't think derating should be a deterent to installing more branch circuits.
    Steve
    [ April 29, 2005, 09:22 AM: Message edited by: steve66 ]
  2. #12
    Join Date
    Dec 2003
    Houston, Texas
    Posts
    48
    Several years and editions ago when load diversity was a part of 310-15 we used a load diversity of 50% when; not more than 50% of the conductors in a given raceway or cable were current carrying at the same time.
    If the number of current carrying conductors is greater than 50% of the total number of conductors, the formula in B.310.11 must be used.
    If the number of current carrying conductors is less than 50%, the formula may be used.
    If the number of current carrying conductors is 50% of the total the table may be used.
    We used this when we had a lot of interlocked loads that prevented conductors being energized.
  3. #13
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,778
    If, for example, you have 8 wires in a conduit (i.e., two sets of A, B, C, N), and if there is a control mechanism (i.e., an interlock) that allows only 3 of the wires (plus its associated neutral) to carry current at a time, then I believe you can simply say that the number of current-carrying conductors is 3, and not 6. You would not have to correct per Table 310.15(B)(2)(a). But that has nothing to do with “load diversity.”
    The phrase “diversity factor” (ASIDE: Is that the same thing as “load diversity”? I do not know.) is defined as “The ratio of the sum of the individual maximum demands of the various subdivisions of a system to the maximum demand of the whole system.” If anyone can figure out how to apply this definition in a useful way (i.e., to get more ampacity out of an installation), then I would love to hear about the method.
    To Steve66: Regarding your “what if?” situation: The difference between the number (or total rating) of the circuits you install, as compared to the VA per square foot allowance that 220 requires us to include, is unrelated to “diversity factor,” as defined above. But no knowing what is meant by “load diversity,” I can’t comment on your “what if.”
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  4. #14
    I was fortunate enough to be the staff liaison for Code Panel 6 when all these new rules and Neher-McGrath calculations were introduce in the Code. Load Diversity is defined in the IEEE Dictionary as the difference between the sum of the maximum of two or more individual loads and the coincident or combined maximum load over a specific period of time. Diversity as used in the Code, means the percentage of energized conductors in a raceway or cable. For example, there is a 50 % diversity when 10 or more conductors are in a cable or raceway. Diversity here means the percent of energized conductors in the cable or raceway.
  5. #15
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,778
    Originally posted by john m. caloggero: Load Diversity is defined in the IEEE Dictionary as the difference between the sum of the maximum of two or more individual loads and the coincident or combined maximum load over a specific period of time.
    That is essentially the same as the definition I quoted above for “diversity factor.” A distinction between your definition and mine is in the use of the word “difference,” as opposed to “ratio.” But I think the intent is the same for both cases.
    If that is true, then it is not related to the definitions that you and I have quoted. “Load Diversity” and Diversity Factor” are related to measured, maximum currents, not to whether or not a conductor is energized (or whether or not it is carrying current).
    But your description of the intended use of “Load Diversity” does not make sense to me. A cable can be “energized,” and still not carry current. If there are no devices plugged into any receptacle outlets throughout a house, the conductors that serve those outlets are still “energized.” On the other hand, if you meant to say “carrying current,” instead of the conversational shorthand “energized,” that would still not clarify the issue. That is because the code does not distinguish between conductors carrying a little current and those carrying their maximum current, when it addresses ampacities.
    I think I understand now what Don said about a lack of agreement on the meaning of the phrase.
  6. #16
    Table 310.15(B)(2)(a) is applicable to three or more current-carrying conductors in a cable or raceway where all of the conductors are carrying current simultaneously. The 50 percent load diversity addressed pertains to Table B 310.11 in annex B for 10 or more current-carrying conductors where only 50 percent of the conductors are carrying current simultaneously. An example might help: Assume 30 conductors with a table ampacity of 20 amps installed in a raceway and assume 1 ohm resistance. The percentage from Table B.310.11 is 60%, therefore, 0.6 x 20A = 12A. Fifty percent diversity means that only 15 are carrying current. I^2R(15)=watts.
    12^2 x 1 x 15 = 2160 watts of heat. The calculated value can not be exceeded by any other combination of conductors or conductor ampacities. If 25 of the 30 conductors are carrying current at 50% of their ampacity 50% of 20A = 10A. Therefore, 10^2 x 1 x 25 = 2500W which is higher than the allowable heat of 2160W.
Posting Permissions
  • You may not post replies
  • You may not edit your posts