Manhole entry PPE

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What PPE is required, other than the normal confined space entry PPE, is required to enter a manhole that contains energized 5kV shielded cables? The purpose of the entry would be to remove and replace a faulted cable.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Bill,
That is all the standard confined space stuff...is there anything that is required just because the manhole contains insulated energized 5kV cables?
 

billsnuff

Senior Member
70E table 130.7C9a Other equip over 1kV Insulated Cable examination, in manhole or confined space.......HRC 4....... gloves Yes



(I don't work w/anything over 480/277)
 