A GEC has to be continuous between the neutral connection at the service to the grounding electrode. Beyond that, the conductors that connect grounding electrodes together are "bonding jumpers" which must be installed according to 250.53(C).stew said:Am I overthinkig this ? how about 250.64 (c)? continous and without splice? I always thought that the gec had to be continous no?
250.53(C) requires the bonding jumpers to comply with 250.64 (A), (B), and (E).
250.64(F) allows us to run to a convenient grounding electrode, or each electrode individually.
250.64(C)(3) allows us to substitute a busbar for the first grounding electrode, and install bonding jumpers from that point.