Crouse-Hinds is now Who????

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Today we had the building inspector request we change a main breaker in a crouse hinds meter-main vintage 1980's. I believe they were bought out by Murray-Siemans in the 90's. I had a Murray MP-T 100 on the truck , but I am not sure if this is a exceptable replacement.If anyone has a referance I can use I would be very appreciative. The old main was a 2pole 100 JA crousehinds. The common trip tie on the handle was snapped off.
 

mdshunk

Senior Member
Location
Right here.
The Cutler Hammer classified replacement breakers are checked out for pretty much all the "Westinghouse style" breakers. They are approved for GE, Siemens, Murray, Thomas and Betts, Square D Homeline, and Crouse-Hinds panels. Their regular BR breakers are already okay for Bryant, Westinghouse, and Challenger.

http://www.eatonelectrical.com/unsecure/cms1/SA00304001E.PDF

Murry/Seimens/ITE is the direct replacement for Crouse-Hinds now.
 