What is a nonmetallic extension?Is it the same as nm cable?
Article 382.
I am going to be inspecting a very old office building in the near future.
They are going to do some remolding.The plan is to install a new breaker panel in the rear of the building.The existing panel is in the front.They want to use the existing panel as a "J" box and run a conduit back to the new panel.Probably 6 circuits max.
My question is can they reuse the old 2/wire nm(no grounding conductor)?They would of course leave any 2/wire receptacles as 2/wire.The new wire installed in the conduit would contain an equipment grounding means.I would like some other peoples thoughts
Thanks Paul
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's basically a zip cord with an outlet on the end. See them a lot in old houses where there may be only one receptacle in a room. Someone staples this zip cord to the baseboard and plugs it into the receptacle. The end usually has two or three two prong receptacles in it.
 