250.64(D)/2002 permits tap conductors.
For what reason would the "TAP" not be allowed in the service disconnect enclosure?
Scenario:
400A service composed of 2-200A MB panels, each fed by #4/0AL SEU from meter base.
GEC #1/0AL, TAP conductors #2AL sized per 250.66 Note#1.
Why can't the #1/0AL GEC be run and terminated to the ground/neutral bar of one panel and the #2AL TAP conductor terminated on the same ground/neutral bar and be routed to and terminated at the other panel?
OR
Same scenario, except both panels have a PVC nipple between them.
Why can't GEC be routed into one panel and connected to the TAP conductors with a split bolt (as would be done on the outside of the panel) connector. The TAP conductors would then be routed and terminated at the ground/neutral bar of each respective panel. One would travel through the nipple to the other panel.
I usually make the TAP to the GEC on the outside of the panel and route the TAP conductors to each enclosure as specified in the Code Section.
This becomes a problem when the panels are flush with the finnished surface as the TAP must be accessable.
Just contemplating other options.
For what reason would the "TAP" not be allowed in the service disconnect enclosure?
Scenario:
400A service composed of 2-200A MB panels, each fed by #4/0AL SEU from meter base.
GEC #1/0AL, TAP conductors #2AL sized per 250.66 Note#1.
Why can't the #1/0AL GEC be run and terminated to the ground/neutral bar of one panel and the #2AL TAP conductor terminated on the same ground/neutral bar and be routed to and terminated at the other panel?
OR
Same scenario, except both panels have a PVC nipple between them.
Why can't GEC be routed into one panel and connected to the TAP conductors with a split bolt (as would be done on the outside of the panel) connector. The TAP conductors would then be routed and terminated at the ground/neutral bar of each respective panel. One would travel through the nipple to the other panel.
I usually make the TAP to the GEC on the outside of the panel and route the TAP conductors to each enclosure as specified in the Code Section.
This becomes a problem when the panels are flush with the finnished surface as the TAP must be accessable.
Just contemplating other options.