Conduit straping question?

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Is the code 3' from a j-box , condulet or coupling?Someone told me you dont have to be 3' from a coupling?Also is there any difference between emt and imc and rmc?Thank you.
 

mdshunk

Senior Member
Location
Right here.
Within 3 feet. It could be one inch, if you wanted to go nuts about it.

edit... nevermind... I see you're asking specifically about distance from couplings.
 

celtic

Senior Member
Location
NJ
This goes back to at least the '99 edition...
Raceways not Required to be Supported Withing 3 ft of Couplings, Section 348-13

348-13.gif


358.30 ['02 - '08]
35830.jpg


The rules are pretty much the same for conduits and tubing.
 

cadpoint

Senior Member
Location
Durham, NC
3' is the Maximum attachment limit, I perfer to go about 24" so I don't make the AHJ break out their tape. When you go up to 30" and beyond the it starts to look long, or in this case two far for the eye to measure. Sometime I'll make a story pole to keep a constant measurement around if doing exposed work.
It just looks simple and professional to have a constant flow of straping.
JMO.
article 358 is for EMT Light gage steel with aluminum coating
article 342 is for IMC a little heavier steel that threadable.
Article 344 is for RMC real Steel also threadabke and also can have various protective coatings.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would add that under the 2008 for some conduits, unbroken conduit sections 18" or less require no support.
 