Default Tranformer Testing

Drawing a blank !
What is the calculation needed to test for correct resistance on a tranformer without load?
I.E. 480 volt 150 VA single phase control transfomer with a 120 volt secondary.
  #2  
Old 07-08-2003, 03:00 PM
bennie bennie is offline
Senior Member
 
Join Date: Feb 2003
Posts: 3,172
Default Re: Tranformer Testing

ANSI/IEEE C-57 publication has the testing method for resistance measuring.

Basically it is with a Wheatstone bridge, or a battery, and voltmeter/ammeter configuration.

The standard is C57.12.91.1979
  #3  
Old 07-08-2003, 03:46 PM
bennie bennie is offline
Senior Member
 
Join Date: Feb 2003
Posts: 3,172
Default Re: Tranformer Testing

I am curious as to why you feel the correct resistance is necessary to know?
  #4  
Old 07-08-2003, 04:00 PM
charlie b's Avatar
charlie b charlie b is offline
Moderator
 
Join Date: Feb 2003
Location: Seattle, WA
Posts: 13,914
Default Re: Tranformer Testing

If you are asking about theory, then the most common formula that is related to this question is that power equals (voltage squared) divided by resistance. That means that resistance will equal (voltage squared) divided by power.

R = (480 x 480) / (150) = 1536 ohms (as seen by the primary)
R = (120 x 120) / (150) = 96 ohms (as seen by the secondary)

Please note that the actual numerical values are approximate, simply because the 150VA, 480V, and 120V are “nominal values.” In order to determine the actual value of resistance for a specific coil, you need to use the test equipment that Bennie has described.
__________________
Charles E. Beck, P.E., Seattle
  #5  
Old 07-08-2003, 04:10 PM
rickcham rickcham is offline
Member
 
Join Date: Apr 2003
Posts: 59
Default Re: Tranformer Testing

You could also try a TTR test, Transformer Turns Ratio to determine if you have the correct winding ratio. This test equipment is easily rented
Only a thought
  #6  
Old 07-08-2003, 04:35 PM
bennie bennie is offline
Senior Member
 
Join Date: Feb 2003
Posts: 3,172
Default Re: Tranformer Testing

Dkelect:

No.#1. Is there other transformers available for comparing the readings?

No.#2. Check with the manufacturer, or go to a distributor and measure a new transformer.

No.#3. Turn this one on and perform a smoke test
  #7  
Old 07-08-2003, 04:54 PM
bennie bennie is offline
Senior Member
 
Join Date: Feb 2003
Posts: 3,172
Default Re: Tranformer Testing

I measured a 150 va, 480/120 volt transformer windings. Any resistance less than 27 ohms plus or minus 3, will indicate shorted turns. There will not be a higher reading except infinity. The lower resistance should produce smoke.

[ July 08, 2003, 07:59 PM: Message edited by: bennie ]
  #8  
Old 07-08-2003, 05:05 PM
bennie bennie is offline
Senior Member
 
Join Date: Feb 2003
Posts: 3,172
Default Re: Tranformer Testing

Shorted turns in a transformer are usually caused by a low side surge. The magnitude of the surge causes a layer to layer failure, involving many turns.

The surge can pass through the windings by capacity coupling and can affect the primary and secondary.

[ July 08, 2003, 07:47 PM: Message edited by: bennie ]
  #9  
Old 07-09-2003, 12:53 PM
dkelect dkelect is offline
Junior Member
 
Join Date: Jul 2003
Posts: 2
Default Re: Tranformer Testing

Actual Transformer Testing Results:

We service a sewage treatment plant.
After a lightning strike that went into the MCC, we had (2) identical control transformers side by side with the fuses blown.
When testing the resistance on the primary side of these transformers (480/120V 150VA)one transformer measured 13ohms the other 27 ohms. We were trying to determine what the proper reading should be.

We did go ahead and energize the transformers.
the transformer with the 27 ohm reading appears to be working ok. The transformer with the 13 ohm reading blew the control fuse. We pulled this transformer and tested it on our bench at the shop.
After a period of testing (with higher amp fuses) the transformer coil opened up. (smoked)
Closed Thread

SpecialBanner1 All Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:47 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.