My brother-in-law is having a discussion with an inspector. Inspector says that the wiring in a wall shared by two apartments must be in conduit.
Is this true? We live in South Carolina. I know the state code may be different as well as the county code, but is this standard. |
|
#2
|
|||
|
|||
|
Ask where he is getting this code as 334.10 Uses Permitted. allows it if the finsh has a 15 min. rating or more. and the party wall in multi-familiy housing must have a 2 hour rating in most ares of the country. so it is allowed as long as anything breaching it must be fire rated caulked and if the N/M breaches this fire wall it must be sleaved. Even plastic nail-on box's have a 1 hour rating.
__________________
Wayne A. From: N.W.Indiana Be Fair, Be Safe Just don't be fairly safe |
![]() |