Results 1 to 9 of 9
Thread: max number of bends
  1. #1
    Join Date
    Apr 2004
    Posts
    26
    max number of bends
    Hey guys, I was trying to find the max # of bends in a 100' of EMT. Also isn't there some little degrees variable in thate equation somewhere?
    Thanks,
    Shaun
    SHAUN \"DAWANNABEELECTRICIAN\"
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Re: max number of bends
    360 degrees max. 1' to 1,000,000'
  3. #3
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    See Article 358.26 of the 2002 NEC for allowed bends in one run of conduit for EMT.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  4. #4
    Join Date
    Apr 2004
    Posts
    26
    thanks guys
  5. #5
    Join Date
    Feb 2003
    Posts
    1,257
    Thanks,
    Shaun
    You must count ALL bends. This includes box offsets, saddles, etc... in your 360 max.
    Todd
    Live Long and Prosper.
  6. #6
    Join Date
    Feb 2003
    San Diego
    Posts
    568
    At one point, I was thinking of proposing a Code change to eliminate the inclusion of the box offset [since is is so small and the the wires {40%} actually go straight thru].
    But one day I pushed a run of about 40' and it had a super bend and then another 90 and then a 22.5 offset and finally the box offset. I got the wires pushed almost all of the way and investigation showed that it got hung up entering that last box offset. So it does make a little difference.
    ~Peter
  7. #7
    Join Date
    Feb 2003
    Portage, Indiana NEC: 2008
    Posts
    9,911
    Luke believe it or not we had a electrician (well he thought he was one) that thought that as long as every bend had a bend in the opposite direction it would cancel the first bend out, so he didn't think it needed to be counted.
    [ April 22, 2004, 02:21 AM: Message edited by: hurk27 ]
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe
  8. #8
    Join Date
    May 2003
    Posts
    6
    Do you know why they decided on 360 degrees of bends? Well it's pretty simple actually, it's because when you have something like a wire or a Horse's Rein,(Yeah just like in the Old Westerns, where they just throw the horses rein over and around the Hitching post) that encounters 360 degrees of friction, it effectively becomes a "CINCH" type Knot. And when you try to overcome that much of resistive friction, you can damage the wire, then you have it to do all over again.
    I worked on a job once where the Specs only allowed 180 degrees of bends, with every bend, no matter how slight, was to be considered a 90 degree bend. Therefore before and after every box offset, we had to install a Pulling "C" type Condulet. Regardless of the type or size of conduit.
    What the Hay, they pay the money, they get it the way they want it.
  9. #9
    Join Date
    Feb 2004
    Posts
    1
    so you have already got your answer, "360 degrees", that is what the answer will be on a test. In practice, as a fellow electrician, when you have on long run with multiple circuits, it is always a good idea to install a pull box.
    Chicago electrician
Posting Permissions
  • You may not post replies
  • You may not edit your posts