Are they required ?
Yes it is.A MA still has sharp edges but do they need a bushing ? I don't think they were designed to not need them.eric stromberg said:bushings?
It seems a little vague. Check out 352.46
infinity said:The question is do PVC terminal adapters have a "smoothly rounded" edge?
iwire said:infinity said:The question is do PVC terminal adapters have a "smoothly rounded" edge?
Trevor what about 352.46?
352.46 Bushings.
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.
FPN: See 300.4(F) for the protection of conductors 4 AWG and larger at bushings.
Pierre C Belarge said:Did you notice that I am now starting over again with the number of posts?? I was demoted friday by the webmaster.... I tried to change my profile and could not log on for days... so they changed my status.
I am now a GREEN HORN
Pierre C Belarge said:Did you notice that I am now starting over again with the number of posts?? I was demoted friday by the webmaster.... I tried to change my profile and could not log on for days... so they changed my status.
I am now a GREEN HORN
Pierre C Belarge said:Did you notice that I am now starting over again with the number of posts?? I was demoted friday by the webmaster.... I tried to change my profile and could not log on for days... so they changed my status.
I am now a GREEN HORN
georgestolz said:I just figured there was another Pierre Belarge here. Not like it's an unusual name or something.
don_resqcapt19 said:Why do most use male terminal adapters with locknuts and bushings in place of box adapters?.
Don