M. D.
Senior Member
Augie confused me , not that he meant too or that it is hard to do ,..but I now have a question.
So we have a service feeding an outside disconnecting means consisting of two breakers ,, one is a branch circuit feeding an AC all outside. The other is a 200amp breaker feeding a panelboard inside the dwelling the service is 4/0 al what size would the feeder to the panel need to be ??
I see only one feeder so 4/0
FEEDER All circuit conductors between the service equipment...... and the final branch circuit overcurrent device
So we have a service feeding an outside disconnecting means consisting of two breakers ,, one is a branch circuit feeding an AC all outside. The other is a 200amp breaker feeding a panelboard inside the dwelling the service is 4/0 al what size would the feeder to the panel need to be ??
I see only one feeder so 4/0
FEEDER All circuit conductors between the service equipment...... and the final branch circuit overcurrent device