#1
|
||||
|
||||
|
Is there any Code requirement that a supplementary rod electrode cannot be located inside a building? Example would be a house with a crawl space with a dirt floor.
|
|
#2
|
||||
|
||||
|
I do not believe there is any restriction that says it has to be outside. I see them inside of commercial and industry.
|
|
#3
|
||||
|
||||
|
No problem, sorta. The Code is a permissive document, in other words, if it doesn't say you can't, then you can. In the case of a ground rod in the crawl space, how do you deal with the dryness issue in the future when the soil dries out? I know the rod extends down about 10 feet (length of the rod plus the depth of the crawl space), but I would think it would still be dryer than the surrounding area. Remember the Code is a minimum standard. I would not feel comfortable with the idea. :(
__________________
Charlie Eldridge, Indianapolis, Utility Power Guy Responses based on the 2008 NEC, unless stated otherwise.
|
|
#4
|
|||
|
|||
|
There is no restriction as long as you meet the requirements of 250.53(D)(2) and (E), (G) if supplementing underground metal water pipe, or 250.54 and 250.118.
__________________
Bryan P. Holland, ICC Electrical Code Official CBO, Plans Examiner, Inspector, Instructor Secretary - IAEI Florida Gulf Coast Division Secretary - BOAF Gulf Coast Chapter |
|
#5
|
||||
|
||||
|
Charlie: In this case the rod would be an additional 4' below outside grade due to the crawl space depth and next to the foundation outside wall. Becuse of this I believe the ground resistance would be less in this case.
Al |
|
#6
|
|||
|
|||
|
By chance I found an answer to this from Charlie Trout (Code Message of the Day) from 2000. He says it is allowed but questions why you would want to direct a lightning strike to that point. He adds that driving two rods might save time rather than having to prove a 25 ohm resistance from the rod in dry soil.
Karl
__________________
Karl Riley Moderator |
|
#7
|
|||
|
|||
|
Are we talking supplemental electrode or supplementary electrode there is a difference.
ie, supplemental electode 250.56 and suplementary grounding electrodes and their conductors are not required to comply with the bonding requirements of article 250.50/ Supplementary electrodes are usually used for signal reference 250.54. WOC |
![]() |