Is there any Code requirement that a supplementary rod electrode cannot be located inside a building? Example would be a house with a crawl space with a dirt floor.
  #2  
Old 02-28-2003, 09:32 AM
dereckbc's Avatar
dereckbc dereckbc is offline
Moderator
 
Join Date: Feb 2003
Location: Plano, TX
Posts: 3,328
Default Re: Ground Rod Inside Building

I do not believe there is any restriction that says it has to be outside. I see them inside of commercial and industry.
  #3  
Old 02-28-2003, 09:33 AM
charlie's Avatar
charlie charlie is offline
Moderator
 
Join Date: Feb 2003
Location: Indianapolis
Posts: 6,098
Default Re: Ground Rod Inside Building

No problem, sorta. The Code is a permissive document, in other words, if it doesn't say you can't, then you can. In the case of a ground rod in the crawl space, how do you deal with the dryness issue in the future when the soil dries out? I know the rod extends down about 10 feet (length of the rod plus the depth of the crawl space), but I would think it would still be dryer than the surrounding area. Remember the Code is a minimum standard. I would not feel comfortable with the idea. :(
__________________
Charlie Eldridge, Indianapolis, Utility Power Guy
Responses based on the 2008 NEC, unless stated otherwise.
  #4  
Old 02-28-2003, 09:34 AM
bphgravity bphgravity is offline
Senior Member
 
Join Date: Feb 2003
Location: Florida
Posts: 6,951
Default Re: Ground Rod Inside Building

There is no restriction as long as you meet the requirements of 250.53(D)(2) and (E), (G) if supplementing underground metal water pipe, or 250.54 and 250.118.
__________________
Bryan P. Holland, ICC Electrical Code Official
CBO, Plans Examiner, Inspector, Instructor
Secretary - IAEI Florida Gulf Coast Division
Secretary - BOAF Gulf Coast Chapter
  #5  
Old 02-28-2003, 09:59 AM
al's Avatar
al al is offline
Senior Member
 
Join Date: Feb 2003
Location: Minnesota
Posts: 143
Default Re: Ground Rod Inside Building

Charlie: In this case the rod would be an additional 4' below outside grade due to the crawl space depth and next to the foundation outside wall. Becuse of this I believe the ground resistance would be less in this case.
Al
  #6  
Old 02-28-2003, 01:13 PM
karl riley karl riley is offline
Moderator
 
Join Date: Feb 2003
Posts: 619
Default Re: Ground Rod Inside Building

By chance I found an answer to this from Charlie Trout (Code Message of the Day) from 2000. He says it is allowed but questions why you would want to direct a lightning strike to that point. He adds that driving two rods might save time rather than having to prove a 25 ohm resistance from the rod in dry soil.
Karl
__________________
Karl Riley
Moderator
  #7  
Old 03-02-2003, 11:34 AM
wocolt wocolt is offline
Member
 
Join Date: Feb 2003
Location: Ohio
Posts: 79
Default Re: Ground Rod Inside Building

Are we talking supplemental electrode or supplementary electrode there is a difference.
ie, supplemental electode 250.56 and suplementary grounding electrodes and their conductors are not required to comply with the bonding requirements of article 250.50/
Supplementary electrodes are usually used for signal reference 250.54.

WOC
Closed Thread

CEU Banner Home Page

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 08:09 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.