Cavie
Senior Member
- Location
- SW Florida
I am finding many top end ranges requireing 50 amp circuits and cook tops requiring 40 amp circuits. 210.19 allowes 40 and 30 amp circuits for these applications. The install instructions call for the larger ampasities. The argument is that the full load will never be used. I have been told to egnore this by my AHJ and move on but then I am told to use 110.3 (B) if I find different manufactours breakers in panels. What's a person to do?