Thread: Subpanel grounding

  1. #1
    Join Date
    May 2003
    Posts
    23

    Subpanel grounding

    I have a house that was feed over head from a remote pole service to the old type service entrance 3 wire cable which ran into the main panel. This panel was grounded with a rod. Later an addition was added at the point where the over head drop attached to the house so the drop was relocated to the far end of the new addition and a new main panel was added at this point. It to was grounded with a rod. This now made the original panel a subpanel and they feed it from the new panel with 3 wire ( 2 hots/1 n ).My ? is,#1 does code require a ground wire bonding between rods and panels.#2 If so is the separation of the grounding bus & the neutral bus required in the subpanel.#3 Can the subpanel be treated the same as a subpanel noted in 250.32/A of the NEC which allows either a grounding rod or a pulled bonding wire.
    My inspector wants home owner to pull in a bonding wire and I fell they are safe with the rods at each panel.

  2. #2
    Join Date
    Feb 2003
    Location
    Maryland
    Posts
    283

    Re: Subpanel grounding

    In order to guard against the possibility of a high impedance condition on the neutral conductor between two panels located in the same building the separate Equipment Grounding Conductor (EGC) is required. With a separate EGC and the neutral of the feeder kept aloof from ground at all points beyond the service disconnect you can avoid having neutral currents flowing on interior metal piping and other metallic systems and structural components that are not designed to carry current. The code permits the use of the second ground rod at the feeder supplied panel but it may only be connected to the EGC at that point and not to the grounded conductor.

    250.54 Supplementary Grounding Electrodes.
    Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.

    #1 does code require a ground wire bonding between rods and panels.
    The Code requires an EGC between the two panels that is run with the feeder conductors in the same raceway or cable.

    #2 If so is the separation of the grounding bus & the neutral bus required in the sub panel.
    Yes, you must keep them separate.

    250.24 Grounding Service-Supplied Alternating-Current Systems.
    (A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
    (5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.

    #3 Can the sub panel be treated the same as a sub panel noted in 250.32/A of the NEC which allows either a grounding rod or a pulled bonding wire.
    The answer to this question is contained in the title of the article you are asking about. It reads "250.32 Two or More Buildings or Structures Supplied from a Common Service." You are not talking about two buildings but rather two sections of the same building. Even if it were two buildings it would need to be free of any other metallic pathways between the two structures in order to be acceptable without an EGC that is run with the feeder in the same raceway cable or trench.

    It is also worth noting that, in the case of separate buildings, if there is more than a single branch circuit to the second building it is required to have a grounding electrode system regardless of whether or not an EGC was run with the feeder. So it is not a choice between a "either a grounding rod or a pulled bonding wire" but rather a choice between whether or not to run an EGC to a separate building that is free of any metallic pathways between it and the building in which the feeder supplying it originates.
    --
    Tom

    [ May 03, 2003, 03:58 PM: Message edited by: hornetd ]
    Tom Horne

    "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

  3. #3
    Join Date
    May 2003
    Posts
    23

    Re: Subpanel grounding

    Tom
    Thanks,
    The problem I have is that house is a flattop with a slab floor so getting a EGC between panels well be costly.The owner has little money and is very old so I'm tring to make it as safe as posible for her and still stay some what in the scope of the code. We sometimes must balance the 3 C's- Code/Cost&Commom Sense.
    Bob

  4. #4
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    6,645

    Re: Subpanel grounding

    Remember the grounded neutral conductor is a current carrying conductor. If you reground the neutral at a subpanel, some of the neutral current will flow on any conductive metal. Conduit connectors are not designed to carry current, they will heat and cause the wood to dry out and start a fire.
    Mike Holt has a video "open neutrals" that shows how this happens in houses with the power shut off, several duplexes had fires from low voltages of 10-15 volts for long periods of time from pyrophoric carbonization. You can order the video from his office its about $20.
    Moderator-Washington State
    Ancora Imparo

  5. #5
    Join Date
    May 2003
    Posts
    23

    Re: Subpanel grounding

    Tom
    If I treat the second panel as a subpanel as required and separate the ground and neutral bus, this well put the EGC on the subpanel ground rod and put the neutral on the main service grounding system (the water line is also bonded at that point). Since there are no metallic ties between the main part of the house and the addition (the house is wired in romex), Does not that give me the required fault to ground protection needed at the subpanel and is not that the purpose of the prescribed forth wire (EGC). I feel that the ground rod at the subpanel would better service the purpose of fault dispersal then a long EGC conducter. Where am I wrong?
    Thanks for the heads up on video-I well get one.
    Bob

  6. #6
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    1,250

    Re: Subpanel grounding

    250.4 General Requirements for Grounding and Bonding.
    (A) Grounded Systems.
    (5) Effective Ground-Fault Current Path.


    The earth shall not be used as the sole equipment grounding conductor or effective ground-fault current path.

    David

  7. #7
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,310

    Re: Subpanel grounding

    Bob,
    I feel that the ground rod at the subpanel would better service the purpose of fault dispersal then a long EGC conducter.
    A ground rod will almost never be able to clear a fault. The inpedance of the earth will limit the current to a level too low to open the overcurrent protective device. When I teach a grounding class, sometimes I have them install a 10' rod in the yard. We then connect to the hot wire from a 15 or 20 amp circuit to the rod and put a amp-clamp on the wire. It has never tripped the breaker and the most current I've ever read on the meter was 7 amps and that was after 3 days of heavy rain. The grounding electrode system is only intended to help provide protection from faults outside of the system, like lightning or a high voltage line contacting the 120/240 volt lines.
    Don
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  8. #8
    Join Date
    Feb 2003
    Location
    Maryland
    Posts
    283

    Re: Subpanel grounding

    If you read the NEC section I have quoted below very carefully you will see that the purpose of grounding is not to clear faults within the grounded system but rather to limit the voltage to ground during a fault, do to lightning, or during accidental contact with distribution lines. Items three and four accurately describe the circuits used to clear faults within the system as bonding. This is the reason that Don Ganiere, who goes by the nom de plume don_resqcapt19 on this forum, wrote a proposal that is now under consideration by several code making panels to change the term "Equipment Grounding Conductor" to "Equipment Bonding Conductor." This would be a tremendous step forward in changing the industry's understanding of the purpose of grounding.

    "250.4 General Requirements for Grounding and Bonding.
    The following general requirements identify what grounding and bonding of electrical systems are required to accomplish. The prescriptive methods contained in Article 250 shall be followed to comply with the performance requirements of this section.
    (A) Grounded Systems.
    (1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.
    (2) Grounding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected to earth so as to limit the voltage to ground on these materials.
    3) Bonding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
    (4) Bonding of Electrically Conductive Materials and Other Equipment. Electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
    (5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a permanent, low-impedance circuit capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be used as the sole equipment grounding conductor or effective ground-fault current path." ©2002 National Fire Protection Association.
    --
    Tom

    [ May 08, 2003, 04:14 PM: Message edited by: hornetd ]
    Tom Horne

    "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

  9. #9
    Join Date
    May 2003
    Posts
    23

    Re: Subpanel grounding

    Tom
    The bulb is becoming brighter but not to full glow yet :-).
    I understand what you are saying and it goes against my understanding of the perpose of the ground. Can't beleive I went 30 years not knowing this.
    Now that you have destroyed all my theories, tell me where does the fault dissipate to.
    Bob

  10. #10
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,310

    Re: Subpanel grounding

    Bob,
    A fault is no different than any other circuit. The current must return to the source to have a circuit. In a grounded system with a ground fault, the current must have a path back to XO at the transformer.
    Don
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin