Thread: Lightning Protection for Building

  1. #1

    Lightning Protection for Building

    What is the minimum requirement in the code on Lightning protection?

    Is there a minimum height of the building wer lightning protection should be installed?

    How do i determine if lightning protection is required? or not required

  2. #2
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    6,646

    Re: Lightning Protection for Building

    Lightning protection, is not an NEC issue, there are a few references to lightning in the NEC, see this footnote in Art 250
    FPN No. 1: See 250.60 for use of air terminals. For further information, see NFPA 780-1997, Standard for the Installation of Lightning Protection Systems, which contains detailed information on grounding, bonding, and spacing from lightning protection systems.
    Lightning protection is an optional installed system. Its the risk versus the cost.
    Moderator-Washington State
    Ancora Imparo

  3. #3
    Join Date
    Feb 2003
    Location
    Plano, TX
    Posts
    3,770

    Re: Lightning Protection for Building

    Lightning protection is not an NEC requirement.

  4. #4
    Join Date
    Feb 2003
    Location
    Plano, TX
    Posts
    3,770

    Re: Lightning Protection for Building

    OOPS, sorry Tom, your post was not visible when I replied.