troyalot

Member
what are the lashing requirements for service entrance conductors ,line side of main fusing, where they enter a 60 inch "top hat" box on top of the gear. there is about 5-6 feet of conductor from the mouth of the pipes to the main lugs. I feel they need lashing to hold them under a fault condition, but is it required and what is common practice. there are 6 parallel runs of 600kcmil. 3phase 208/120.
 

troyalot

Member
Re: lashing of service

has anyone built a service where the conductors needed lashing(securing). i know that typically the length is such that it is not necessary. however i have an unusual situation here. the service entrance(underground pvc) enters the basement at 12 feet above the floor and 6 feet above the lugs. so i have a factory "pull box" full of unfused service conductors hanging freely for 6 feet. any suggestions ?
 

pierre

Senior Member
Re: lashing of service

314.28(B) Conductors in Pull or Junction Boxes.
In pull boxes or junction boxes having any dimension over 6 ft , all conductors shall be cabled or racked up in an approved manner.

Troy
I have seen the use of Kindorf with tywraps and rubber on the Kindorf used in the box to support the conductors, there are other means. I have also seen the use of fiberglass supports.

[ February 28, 2006, 10:21 PM: Message edited by: pierre ]
 

tom baker

First Chief Moderator
Staff member
Re: lashing of service

I have lashed conductors in an MCC and a CT can, both per the mfgs requirements.
The CT Can took about 200 ft of 1/2" nylon rope, sure looked nice when I was done.
For the HAT box check the instructions.
For the second question, I would ask whats the available fault current? The fault current is the basis for lashing.
 

stevearne

Senior Member
Location
Rapid City, SD
Re: lashing of service

This is not an Instructor topic, so it is being moved to an NEC thread. Please feel free to continue your discussion there. :)
 

benaround

Senior Member
Location
Arizona
Re: lashing of service

Troyalot,

I think you just need someone to tell you to do it.

Go get some rope and start doing what you gotta do!
 