SMB
Member
- Location
- North Charleston, SC
I have two 4-wire generators feeding an ATS with an un-switched neutral. All the neutrals connect to a neutral buss at the bottom of the ATS. From the ATS, I go to an MDP. Can I locate my N-G bond prior to the ATS, inside the ATS or does it have to be downstream since the neutral in unswitched? Is this explained in the NEC somewhere? Thanks for any and all responses.