Normally when we wire with "plenum" wire its in an air handling space above a suspended ceiling. Wiring is only allowed inside the plenum (or duct) if necessary to act on the contained air and per 300.22(b).
If you are using the air relief shaft as a wiring chase, I don't belive that is allowed.