I suspect I'll be bludgeoned and abused for this question but I'll ask anyway.
Is there a cross reference of which breakers mount into which panels ? Is it even allowed to have different types in the same panel ? I know each manufacturer specifies that only their breakers can be used in their panel/load centers but I have a situation where there are at least 3 different manufactures represented in the same panel. (GE, Murray, Siemens) Since I'd like to retrofit in some AFCI breakers it would be good to know what style breakers would fit into the panel. A cross reference of what breakers are the same fit and function would be quite helpful. Or is this something that an inspector would see and smack me with the nearest 2x4 ? |
|
#2
|
||||
|
||||
|
The only violation that could be cited would be 110.3(B) if it applies. If you are using breakers that have been listed for interchangability, there is no violation. You might try getting on the manufacturer's website to see if they have the listing information.
Just remember that just becasue a breaker physically fits in the panel does not always mean that it is listed and labeled for the purpose.
__________________
Ryan Jackson, Salt Lake City Inspector, Instructor |
|
#3
|
||||
|
||||
|
If an inspector is influenced by manufacturer rhetoric, he will not allow the "classifeied" (not sure of term) c/b's.
Some manufacturer reps have a real problem with those breakers and claim a big safety issue. How can that be though if UL evaluated it and found it acceptable?
__________________
Larry LeVoir I\'m an Inspector, what do I know? |
|
#4
|
||||
|
||||
|
Quote:
__________________
Ryan Jackson, Salt Lake City Inspector, Instructor |
|
#5
|
|||
|
|||
|
I'm pleased that the consensus seems to be that if the UL/NEC ratings are the same, and it fits in the panel, then "any" breaker should be OK. But no one has indicated that a cross reference for residential type CB's is available.
I may just have to try the self education/trial and error route. It won't be the first time. |
|
#6
|
||||
|
||||
|
I searched for about 10 minutes and couldn't find a good list. You may have to search by the individual manufacturer. For example, I found this press release from Siemens showing that they have a listed replacement for Sqaure D QO breakers:
http://www.sea.siemens.com/resident/product/S3013.pdf
__________________
Ryan Jackson, Salt Lake City Inspector, Instructor |
|
#7
|
|||
|
|||
|
I think you may be misunderstanding some of the replies here. No one is saying that "if it fits, it is OK". What they ARE saying is "if it fit AND is listed for use in the panel you intend to use it in" THEN it is OK. For example, Cutler Hammer has a "classified" breaker that is listed for use in virtually every panel that it will physically fit into. However, a Sq. D Homeline breaker, although it fits into a Siemens panel, is NOT listed for that use.
|
|
#8
|
||||
|
||||
|
Actually no breaker is UL "listed" for use in another makers panel.
UL "Classifies" breakers for use in other panels, For you to be able to do this the model number of the panel must be on the literature included with the replacement breaker. If the model number of your panel is not on the literature you are out of luck.
__________________
Bob |
|
#9
|
||||
|
||||
|
From the UL White Book
CIRCUIT BREAKERS, MOLDED-CASE, CLASSIFIED FOR USE IN SPECIFIED EQUIPMENT (DIXF) GENERAL This category covers Classified molded-case circuit breakers rated 15 to 50 A, 120/240 V maximum that have been investigated and found suitable for use in place of other Listed circuit breakers in specific Listed panelboards. The circuit breakers are Classified for use in specified panelboards in accordance with the details described on the circuit breaker or in the publication provided therewith. In addition, Classified molded-case circuit breakers may also be Listed with additional features such as a ground-fault trip element, ground-fault circuit interrupter, arc-fault circuit interrupter, secondary surge arrester, transient voltage surge suppressor, and the like. PRODUCT MARKINGS A circuit breaker that is Classified only is marked on the side with the statement: ‘‘Classified for use only in specified panelboards where the available short-circuit current is 10 kA, 120/240 volts ac or less. Do not use in equipment connected to circuits having an available system short-circuit current in excess of 10 kA, 120/240 volts ac. For catalog numbers (or equivalent) of specified panelboards, refer to Publication No.______ provided with this circuit breaker. If additional information is necessary, contact [Classified circuit breaker manufacturer’s name].’’ A circuit breaker that is both Classified and Listed is marked on the side with the statement: ‘‘This circuit breaker is Listed for use in circuit breaker enclosures and panelboards intended and marked for its use. This circuit breaker is Classified for use, where the available short-circuit current is 10 kA, 120/240 V ac or less, in the compatible panelboards shown in Publication No. ______ provided with this circuit breaker. When used as a Classified circuit breaker, do not use in equipment connected to circuits having an available system short-circuit current in excess of 10 kA, 120/240 V ac. If additional information is necessary, contact [Classified circuit breaker manufacturer’s name].’’ The referenced publication is a compatibility list which tabulates the company name, catalog number, number of poles and electrical ratings of the Classified circuit breaker, in addition to the company name and catalog number of the applicable UL Listed panelboards, and corresponding UL Listed circuit breakers in place of which the Classified circuit breaker has been investigated. The compatibility list also details the maximum permissible voltage and maximum available short circuit current of the supply system to the panelboard. The Classified circuit breaker is not suitable for the specified application if the system supply characteristics exceed the maximum values indicated in the compatibility list. One copy of the compatibility list is provided with each circuit breaker. Circuit breakers which are both Classified and Listed have markings as above, with the addition of the Listing Mark, located on the side of the circuit breaker. RELATED PRODUCTS For information on markings, see Molded-case Circuit Breakers and Circuit Breaker Enclosures (DIVQ) and Circuit Breakers (DHJR). For those Classified molded-case circuit breakers containing additional features, refer to the following categories: for Arc Fault Circuit Interrupters, Branch/Feeder Type, see AVZQ; for Circuit Breaker and Secondary Surge Arresters, see DIMV; for Circuit Breaker and Transient Voltage Surge Suppressors, see DIPJ; for Circuit Breakers with Equipment Ground Fault Protection, see DIYA; for Circuit Breaker and Ground-fault Circuit Interrupters, see DKUY. ADDITIONAL INFORMATION For additional information, see Circuit Breakers (DHJR) and Electrical Equipment for Use in Ordinary Locations (AALZ). REQUIREMENTS The basic standards used to investigate products in this category are UL 489, ‘‘Molded-Case Circuit Breakers, Molded-Case Switches and Circuit Breaker Enclosures’’ and UL 67, ‘‘Panelboards.’’ LOOK FOR CLASSIFICATION MARK ON PRODUCT The Classification Mark of Underwriters Laboratories Inc. on the product is the only method provided by UL to identify products manufactured under its Classification and Follow-Up Service. The Classification Mark appears on the side of the circuit breaker and consists of the words ‘‘Underwriters Laboratories Inc. Classified Circuit Breaker’’ together with a control number. The words ‘‘Underwriters Laboratories Inc.’’ may be abbreviated ‘‘Underwriters Lab. Inc.’’ or ‘‘Und. Lab. Inc.’’ The following mark: appears on the front, visible surface of the circuit breaker.
__________________
Bob |
|
#10
|
||||
|
||||
|
Quote:
Go to UL's Online Certifications Directory and do a search on Category Code DHJR for the "general" circuit breaker rules. No one actually lists to this category, but it contains important info. Most molded case circuit breakers are listed to Codes DIVQ or DIXF. "DIVQ" gives the most common interchangeability recognitions. (You may want to check the "Design Guide Information Only" box the first time through - you'll get swamped with hits)
__________________
"Bob" Robert B. Alexander, P.E. "I know that you believe you understand what you think the NEC says, but I am not sure you realize that what you read is not what it means.” (Corollary to Charlie’s Rule) |
![]() |