Underground warning ribbon?

Status
Not open for further replies.

dduffee260

Senior Member
Location
Texas
I know that 300.5 (3) states that warning ribbon be placed for service conductors. Is there anywhere else in the code that states that warning ribbon be placed over branch circuit conduits, such as parking lot lights? We have a newbie inspector that wants warning ribbon everywhere under all conduits and I am going to have to argue the point that the warning ribbon is over what is covered in 300.5 (3)
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I am not aware of any NEC requirement for a warning ribbon to be installed over non-service conductors. Maybe there is a local requirement or a job spec.

Chris
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Agreed. It's not a bad idea, but not required. Ask for a code citation, if you don't want to put the ribbon in.

As a general practice, I do anyway - can't hurt. (Of course, I have no idea what the tape costs. :D )
 

mdshunk

Senior Member
Location
Right here.
georgestolz said:
As a general practice, I do anyway - can't hurt. (Of course, I have no idea what the tape costs. :D )
More than you might think, especially in the case of locatable ribbon. I like to sub out the underground conduit work when there's a good bit of it, and the sitework subs tend to put in ribbon on pretty much everything. I sure don't fault a guy if he wants to use some tape. I just don't go out of my way to do so when it's not required.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The answer is simple. If these are service conductors tape is required. For anything else no tape required. Tell the inspector to re-read the section you posted, he's not free to make up his own interpretation.
 