Results 1 to 8 of 8
Thread: Main Disconnect
  1. #1
    Join Date
    Feb 2003
    North Dakota
    Posts
    1
    Main Disconnect
    The main disconnect switch is about 30' away from the control panel. The control panel operates two submersible pumps for a lift station. The pumps have circuit breakers in the control panel. Is there a restriction on how far away the main disconnect switch can be?
  2. #2
    Join Date
    Feb 2003
    Posts
    127
    Re: Main Disconnect
    I believe that the two units must be within sight (up to 50' apart)of each other. See Article 430-102(A)
    Rick Miell
  3. #3
    Join Date
    Feb 2003
    New Hampshire
    Posts
    67
    Re: Main Disconnect
    Unless the two circuit breakers are operable with the control cabinet closed and disconnect their respective pump motor control thus serving as the controller disconnecting means; the main disconnect would become the "controller disconnecting means" and would have to be "in sight" (and less than 50 ft per art. 100 - definitions) of the pump motor controls. art.# 430.102a
    [ February 20, 2003, 07:20 PM: Message edited by: Len_B ]
  4. #4
    Join Date
    Feb 2003
    Posts
    249
    Re: Main Disconnect
    THE BREAKERS MUST ALSO BE ABLE TO LOCKED IN THE OPEN POSITION
    Jeff Cook
    Master Electrician
  5. #5
    Join Date
    Feb 2003
    Illinois
    Posts
    23,574
    Re: Main Disconnect
    There is no NEC requirement for a "lockable" disconenct when the disconnect is within sight of the equipment served by the disconnect.
    Don
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  6. #6
    Join Date
    Feb 2003
    New Hampshire
    Posts
    67
    Re: Main Disconnect
    I agree that there is no "lockable" requirement under NEC, unless exceptions to "in sight" requirements are used for:
    1)controller over 600v --- 430.102a except.1
    2)motor uses controller disconnecting means as motor disc. means --- 430.102b except.
    There may, however, be other lockout requirements under OSHA LO/TO. In addition, NFPA 70E, Standard for Electrical Safety Requirements for Employee Workplaces; or NFPA 79 Electrical Standard for Industrial Machinery, may (I'm not 100% sure) have "lockable" requirements that could also be enforced by OSHA.
    Len
    [ February 21, 2003, 05:04 PM: Message edited by: Len_B ]
  7. #7
    Join Date
    Feb 2003
    Illinois
    Posts
    23,574
    Re: Main Disconnect
    Len,
    I don't think so. OSHA permits tag out without a lock. The utility in our area does not permit the use of any locks on disconnects within their generating plants. Yes, they are not under the NEC, but they are covered by OSHA.
    Don
    Don, Illinois
  8. #8
    Join Date
    Feb 2003
    New Hampshire
    Posts
    67
    Re: Main Disconnect
    Don,
    Thanks. I wasn't sure about possible OSHA requirements that might apply to this specific situation.
    In addition to "in-house" tag only policies, many times locks simply can't be attached, requiring tag out only. BTW, If "tyrap" alone is used for LOTO, I believe it must be 50 pound rated (Code ref ?)
    Len
Posting Permissions
  • You may not post replies
  • You may not edit your posts