    Is there a megger test standard? If somone wants to call for an electrician to test wires insulation where they may or may not have been exposed to damage, is there a testing standard that the electrician should go by?
    "Electrician shall test wiring as per IEEE ???" or somthing along those lines.
    Thanks very much.
  2. #2
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    3,011
    Re: Megger Test Standard
    Electrician shall employ the services of testing agency that is a Full member of The InterNational Electrical Testing Association (NETA) to perform an insulation-resistance test utilizing a megohmmeter. Testing shall conform to the lastest version of the NETA Maintenance Testing Specifications.
    Ron
  3. #3
    Join Date
    Sep 2003
    Posts
    381
    Look at Biddle's web-page on the subject:
    http://www.biddlemegger.com/cgi-bin/..._Analysis.html
    Earl
    Earl
  4. #4
    Join Date
    Sep 2003
    Posts
    381
    How about this?
    IEEE Recommended Practice for Testing Insulation Resistance of Rotating
    Machinery, IEEE Std 43-2000.
    Also for field testing of medium voltage cables:IEEE 400 standard
    And: IEEE P82, the Draft Test Procedure for Impulse Voltage Tests on Insulated Conductors.
    all from the NETA web-site
    Earl