tkb

Senior Member
Location
MA
Someone told me that you cannot have two generators to two transfer switches for one building.

Is this a myth or is it true.
I cannot find it in the NEC 2008.
I looked in the generator section and in the 700's.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
i don't have my code book here so can't say for sure; but i've seen it done.


as long as you're feeding two separate panels, and break the neutrals at the ATS, i don't see a problem.
 

tkb

Senior Member
Location
MA
Why would I need to break the neutral?
We usually use 3 pole 4 wire transfer switches.

These generators are for computer rooms with UPS systems, so I would call them optional standby generators. No life safety.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I am not saying that you can as there may be a prohibiting factor of which I am unaware, but my thoughts would go to 225.30 which limits feeders and "emergency systems" are a "sepcial condition" allowance and I find nothing in Art 702 that prohibits it.
We may both learn somethimg.
 

RUWired

Senior Member
Location
Pa.
I think the plural wording in 225.30(A) allows addition feeders in the special conditions. Otherwise it would say " an additonal feeder".

(A) Special Conditions. Additional feeders or branch circuits shall be permitted to supply the following:

(4) Optional standby systems

Rick
 