    Are circuit breaker types and labels industry standards? That is, can two different companies circuit breakers that have the same designation, but are not compatable with the same equipment?
    I've been running into situations lately where I've needed circuit breakers by manufacturers that no longer exist. I managed to figure out that Cuttler-Hammer makes an acceptable replacement for Bryant circuit breakers. Now I'm looking for Crouse-Hinds and I'm finding a lot of equipment made by Murry that has the same designation, e.g.: MD-A, MP-H etc.
    Does this mean that those breakers are an acceptable replacement for Crouse-Hinds breakers type MD-A, MP-H, etc.?
    Thanks.
    -John
  2. #2
    Join Date
    Feb 2003
    Cleveland, Ohio
    Posts
    1,321
    Re: Circuit Breaker Compatibility
    Hi John,
    To be safe, the replacements need to be listed as replacements for the particular panelboard in question. Either on the panelboard sticker or by the replacement manufacturer.
    Dave Nix
  3. #3
    Join Date
    Sep 2003
    Posts
    969
    Look at the Cutler "CL" breakers. Same physical format as the BR's but UL classified for a bunch of different panels, SQ-D Hom, GE, Siemens, T&B, and Crouse Hinds .
    There's AFCI flavors of the "CL" breakers too.
  4. #4
    Join Date
    Feb 2003
    San Jose, CA
    Posts
    1,477
    Crouse Hinds distribution equipment was renamed back to Murray when Siemens acquired the line. Murray breakers with the same part number can be used in Crouse Hinds equipment. Crouse Hinds equipment was named Murray before it was Crouse Hinds.
    Cutler-Hammer acquired the Westinghouse distribution line which included Challenger. A Cutler-Hammer BR circuit breaker is the replacement for Westinghouse (Bryant) BR circuit breakers and Challenger C breakers. If you look at a BR breaker you will notice that it has both the Westinghouse and Challenger part numbers on it.
    Curt Swartz
    Electrical Contractor
  5. #5
    While breakers from different manufacturers are interchangeable, you should follow the instruction inside the panel cover. The AHJ can site you for improper equipment installation.
    david neuman
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    As long as the breaker itself is UL listed and Classified for a particular panel it can be used in that panel even if that breaker is not listed on the panel cover.
    It has been said on the forum before that there may be warranty issues with contractors installing classified breakers.
    I have never seen any panel manufacture list a competitors breaker on the panel cover, and I doubt they ever will, kind of shooting themselves in the foot if they do.
    Here is the info for some T&B replacement breakers. I only chose T&B because I already had this info in my PC.
    This circuit breaker is listed for use in circuit breaker enclosures and panelboards intended and marked for its use. This circuit breaker is Classified for use, where the available short circuit current is 10kA, 120/240 V ac or less, in the compatible panelboards shown in Publication No. T5651863 provided with this circuit breaker. When used as a Classified circuit breaker, do not use in equipment connected to circuits having an available system short-circuit current in excess of 10 kA, 120/240 V ac. If additional information is necessary, contact Thomas & Betts Corporation, Memphis TN.
    Compatibility List for the Classified Applications Thomas & Betts Corporation
    Listed Breaker TB115C - TB250C 15-50 A 120/240V
    SYSTEM SUPPLY 1 Phase 3 Wire 120/240V
    Max. Short Circuit Current 10kA
    MURRAY
    Listed Breaker MP115-MP250
    Listed Panelboards
    LC112DF/DS
    LC236PC
    LC116DF/DS
    LC240PC
    LC120DF/DS
    JA112CW
    LC220EC/PC
    JA112CY
    LC224EC/PC
    JA224CY
    LC230EC/PC
    JA222CW
    WESTINGHOUSE
    Listed Breaker BR115-BR250
    Listed Panelboards
    S (6-12) C/CG/CD/CDG/R
    S (8-16) C/CG/CD/CDG/R
    B/N/L12 (12-24) CT/CGT
    L/B10 (20-20) CT/R/C
    L/B15 (30-30) CT/R/C
    L/N/B20 (20-40) CT/R/C
    L/N/B20 (30-40) CT/R/C
    L/N/B20 (40-40) CT/R/C
    WMB 10 (12-24) FN /SN/SB
    WMB 20 (20-40) FN/SN/SB
    GENERAL ELECTRIC
    Listed Breaker THQL1115-THQL2150
    Listed Panelboards
    TM2010C/R
    TLM612F/S/R
    TM1212C/CT
    TLM810F/S/R
    TM1210C/R
    TLM812F/S/R
    TM2020C/CT/R
    TM3020C/R
    SIEMENS
    Listed Breaker Q115-Q250
    Listed Panelboards
    G2020MB1100
    E0612ML1125CU
    G2040MB1200
    W0612ML1125CU
    G2440MB1200
    E0812ML1225CU
    G3040MB1200
    W0812ML1125CU
    G3030MB1200
    E0816ML1125CU
    W0816ML1125CU
    CHALLENGER
    LIsted Breaker C115-C250
    Listed Panelboards
    SL12 (6-12) CN/CDN/CDGN/RN
    SL12 (8-16) CN/CGN/RN
    SLB/SL12 (12-24) CCT/CCGT
    SL/SB10 (20-20) CT/R/C
    SL/SB15 (30-30) CT/R/C
    SL/SLB/SB20 (20-40) CT/R/C
    SL/SLB/SB20 (30-40) CT/R/C
    SL/SLB/SB20 (40-40) CT/R/C
    SMB 10 (12-24) FN/SN/SB
    SMB 20 (20-40) FN/SN/SB
    SUITABLE FOR USE IN ALL Thomas & Betts LABELED PANELS
    DO NOT USE IN SERIES RATED SYSTEMS
    Listed
    [ October 09, 2003, 05:44 AM: Message edited by: iwire ]
  7. #7
    Wink circuit breaker compatibility
    Greetings - Iwire yes this is a Thread long in the tooth 10/09/03 was
    your OP.
    Question: Has the SD QO breaker panel, much used in many homes,
    (not there bolt in style, seen in used comerical", now have
    a legal replacement, MFG. by other.
    I believe I have just look into a QO SD panel not to long ago and saw
    such a breaker, only different was, it did not have there red trip flag.
  8. #8
    Join Date
    Sep 2004
    Posts
    1,497
    The only one I've heard of is another classified line from Cutler-Hammer. The CHQ type I believe. Cutler-Hammer seems to make a breaker for just about everyone between their BR, CL, and CHQ lines.
    Mark
    Kent, WA
  9. #9
    Join Date
    May 2003
    Posts
    1,228
    Quote Originally Posted by suemarkp View Post
    Siemens also makes a replacement for a SQ D QO breaker. Except for when a company has changed hands & name(s), makes the most sense to me to just use OEM.