Default conductor size for 240volt air conditioning unit

I am curious as to what size conductor should be used for a 240 volt , 2 1/2 ton a/c unit, in a 1 & 2 family dwelling. I am being told, that 10/2 romex( nm-b) is of sufficient size. I tend to disagree,seeing how the "B" indicates that it is rated for 90 degrees C.. but you would still have to use the 60 degree table for the proper ampacity. yes or no ?
I am also being told that 10/2 romex(nm-b)can fused up to 40 amps for the same application,

[ January 24, 2005, 09:51 PM: Message edited by: nmbme ]
  #2  
Old 01-24-2005, 10:28 PM
drg drg is offline
Senior Member
 
Join Date: Jul 2003
Posts: 435
Default Re: conductor size for 240volt air conditioning unit

See 240.4 (D) for your answer. NEC 2002
  #3  
Old 01-24-2005, 10:29 PM
aelectricalman's Avatar
aelectricalman aelectricalman is offline
Senior Member
 
Join Date: Dec 2004
Location: Bourbontown, KY
Posts: 607
Default Re: conductor size for 240volt air conditioning unit

A 2.5 ton uses about 4400 VA which is about 18-19 Amps for a 240 circuit. You will want to use a 30 Amp circuit. As for the 3 ton (4700VA), you should use a 30 AMPs as well. You will not need a 40 amp cirucit for a 3 ton unit.
__________________
Chris Hill
Hill's Electric Service
Bardstown Kentucky
An Alphaky company
  #4  
Old 01-24-2005, 10:29 PM
electricman2's Avatar
electricman2 electricman2 is offline
Senior Member
 
Join Date: May 2003
Location: North Carolina
Posts: 1,112
Default Re: conductor size for 240volt air conditioning unit

The nameplate will tell you the MCA (minimum circuit ampacity). It will also state the maximum size of the fuse or circuit breaker. Many times this will be above the ampacity of the conductors. It is for ground fault and short circuit protection.
__________________
John, Chair City, NC
Technology: Mans best efforts to make things as good as they used to be
  #5  
Old 01-25-2005, 06:54 AM
charlie's Avatar
charlie charlie is offline
Moderator
 
Join Date: Feb 2003
Location: Indianapolis
Posts: 6,098
Default Re: conductor size for 240volt air conditioning unit

The concept that you need to grasp is that for motors and HVAC equipment, the overload devices for the circuit are in the unit itself, not in the overcurrent device that is protecting the circuit. The device that is protecting the circuit is providing short circuit and ground fault protection, not overload protection.

It is possible to have a #12 Cu. NM protected by a 40 ampere short circuit and ground fault protective device.
__________________
Charlie Eldridge, Indianapolis, Utility Power Guy
Responses based on the 2008 NEC, unless stated otherwise.
  #6  
Old 01-26-2005, 07:03 PM
nmbme nmbme is offline
Junior Member
 
Join Date: Jan 2005
Posts: 26
Default Re: conductor size for 240volt air conditioning unit

O.K. , I guess what I should be asking is , will #10/2 romex be of sufficient size from the O.C.P.D., rated at 35 amps, to the a/c disconnecting means? I realize from the disconnecting means you can use #12 to the unit
  #7  
Old 01-26-2005, 07:23 PM
peter d's Avatar
peter d peter d is offline
Senior Member
 
Join Date: Mar 2003
Posts: 10,075
Default Re: conductor size for 240volt air conditioning unit

Quote:
Originally posted by nmbme: O.K. , I guess what I should be asking is , will #10/2 romex be of sufficient size from the O.C.P.D., rated at 35 amps, to the a/c disconnecting means?
What does the nameplate require for its minimum circuit ampacity?

If the MCA is 30 amps or less, then the 10/2 is fine.
  #8  
Old 01-26-2005, 07:53 PM
busman busman is offline
Senior Member
 
Join Date: Nov 2004
Location: Northern Virginia
Posts: 712
Default Re: conductor size for 240volt air conditioning unit

Also remember that if the nameplate does not say "max size fuse or circuit breaker", but says "max fuse size" then a fuse must be used.

Mark
  #9  
Old 01-28-2005, 11:29 PM
nmbme nmbme is offline
Junior Member
 
Join Date: Jan 2005
Posts: 26
Default Re: conductor size for 240volt air conditioning unit

I fiquired there would be more answers to this , considering the fact that were only talking about an a/c unit. (which could burn a house down if the wire size is not rated for it. I'll say again, what if the min.size amps required is 40 amps , can you still use 10/2 ? how about if the min. was 35 amps ? lol
  #10  
Old 01-29-2005, 07:50 AM
allenwayne allenwayne is offline
Senior Member
 
Join Date: Jan 2005
Posts: 3,034
Default Re: conductor size for 240volt air conditioning unit

I have always used this rule of thumb, wire for min. and fuse/bkr. for max. If the min. ampacity is 35 then # 8 nm is the min.sized conductor allowed.The required ocpd is whatever the nameplate lists as the max.fuse/bkr. size .The conductors that feed the unit must meet ampacity of the min. listed ampacity,NMBME if the min. listed ampacity is 40 then # 8 would be the smallest conductor allowed same for 35 . assuming this is residental and NM is the wiring method .
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 06:58 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.