Results 1 to 7 of 7
Thread: class 2 definition
  1. #1
    Join Date
    Apr 2003
    Posts
    9
    class 2 definition
    What is considered a class 2 rating?
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,870
    Re: class 2 definition
    I don't have my book handy, but what I recall is "less than 30 volts, less than 1000 VA."
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Dec 2003
    New Hampshire
    Posts
    294
    Code:
    Class 2 Circuit. The portion of the wiring system between the load side of a Class 2 power source and the connected equipment.
     Due to its power limitations, a Class 2 circuit considers safety from a fire initiation standpoint and provides acceptable protection from electric shock.
    [ September 02, 2004, 04:13 PM: Message edited by: don_resqcapt19 ]
    Jim
    New Hampshire
  4. #4
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,870
    I remember seeing that definition, but it did not help me understand. It defines “class 2 circuit” by presuming you already know what a “class 2 power source” is. All they need to add in the 2005 version is a definition of a “class 2 power source” as “a source that supplies a class 2 circuit,” and the circular definition will be complete.
  5. #5
    Join Date
    Apr 2003
    Posts
    9
  6. #6
    Join Date
    Apr 2003
    Posts
    9
    Thanks for your help, but I have another quick question for you. Is class 2 a UL or NEC standard?
  7. #7
    Join Date
    Apr 2003
    Westchester County, New York
    Posts
    3,552
    Take a look at 725.41(A).
    A class 2 circuit is defined by it's source, which has to be a listed product.
    A class 2 'rating' is defined by the UL listing.
Posting Permissions
  • You may not post replies
  • You may not edit your posts