Results 1 to 4 of 4
Thread: messenger wire as grounding conductor
  1. #1
    Join Date
    Jul 2005
    Posts
    1
    I believe I recieved my answer from another topic. Just to make sure however... I am running an overhead feeder to a detached garage from the main panel. I'm setting a 240/120 subpanel at garage. So the overhead feeder must be two phases conductors, a grounded neutral, and a grounding conductor. Right? Can the messenger wire be used as the grounding conductor?
  2. #2
    Join Date
    Apr 2003
    Posts
    5,156
    Re: messenger wire as grounding conductor
    I thought it would be easier than this. I guess that's why you're asking.
    First the messenger will have to be acceptable under 250.118 if it's also the EGC.
    396.2 is a definition but it also looks like a requiremet.
    The only thing I'm sure of is that you can use "factory-assembled arial cable".
    Sam, San Francisco Bay Area
  3. #3
    Join Date
    Feb 2003
    Indianapolis
    Posts
    6,102
    The simple answer to your question is yes.
    Charlie Eldridge, Indianapolis, Utility Power Guy
    Responses based on the 2011 NEC, unless stated otherwise.
  4. #4
    Join Date
    Apr 2003
    Posts
    5,156
    I thought it might be.
Posting Permissions
  • You may not post replies
  • You may not edit your posts