20 amp wire on 15 amp breaker?

Status
Not open for further replies.

Libby

New member
If I have a run of 20 amp wire on a 15 amp breaker can I connect the 20 amp wire to 15 amp outlets and switches?
 

allenwayne

Senior Member
I worked for a company that only used #12 wire till they realized the cost factor with using #14.The reason was, but they didn`t admit it at the time was they only had installers well almost only !!!! They used #12 so that it was a no brainer install,install and not have to think.

They also only installed #6/2 for electric heat/A/C, until the issue of a 10K heat strip made them think on that one.But when trim out time came depending on the manufacturers breaker we could use the #6 on a 30 amp or 25 breaker the ones that weren`t rated for that size wire it was a big blue wire nut and a downsized wire.But unless there is a data plate that says max.OCPD 15 amp why even bother.On a receptacle circuit as long as there is more than one single device using a 15 amp receptacle on a 20 amp circuit is good to go.
 

romeo

Senior Member
20 amp wire on 15 amp breaker

20 amp wire on 15 amp breaker

Libby said:
If I have a run of 20 amp wire on a 15 amp breaker can I connect the 20 amp wire to 15 amp outlets and switches?

I agree that it is code compliant. But other than to compensate for voltage drop,what is the advantage? Sounds to me like a home owner doing wiring thinking that he did a great job because he over sized the conductors,then violated the conductor fill. I always felt that wiring to code was normally a safe. However there are always exception to the rules in some cases.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
romeo said:
I agree that it is code compliant. But other than to compensate for voltage drop,what is the advantage? Sounds to me like a home owner doing wiring thinking that he did a great job because he over sized the conductors,then violated the conductor fill. I always felt that wiring to code was normally a safe. However there are always exception to the rules in some cases.
Wiring to code is a minimum. Compensating for voltage drop is very wise in some situations. That is the only advantage one needs to have so don't knock it. I have done this and you can easily do it without overfilling the box. Calculate a 1000 watt heater at a distance of 100 feet from the panel and the formula will suggest a #10 wire to comply with the footnote of 3% voltage drop.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
bikeindy said:
you can use 15A devices even if you use a 20A breaker on a 20A wire, you can not use a 20 A device on a 15 A circuit.


You could use a single 20 amp receptacle on a 15 amp circuit. You cannot use a duplex or multiple receptacles.
 

romeo

Senior Member
20 amp wire on a 15 amp breaker

20 amp wire on a 15 amp breaker

Dennis Alwon said:
Wiring to code is a minimum. Compensating for voltage drop is very wise in some situations. That is the only advantage one needs to have so don't knock it. I have done this and you can easily do it without overfilling the box. Calculate a 1000 watt heater at a distance of 100 feet from the panel and the formula will suggest a #10 wire to comply with the footnote of 3% voltage drop.

Either I was not thorough about my explanation or you miss understood. I said other than to compensate for voltage drop ( that is a good idea ) what is the advantage to over sizing a conductor?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
romeo said:
Either I was not thorough about my explanation or you miss understood. I said other than to compensate for voltage drop ( that is a good idea ) what is the advantage to over sizing a conductor?


Another reason would be for future consideration. We often will run a 10/3 MC cable to dedicated copier receptacle even when the existing machine is 20 amps, and 120 volts. Many times a newer, larger copier will replace the older one and will require a larger circuit. Since the conductors are already oversized a simple change out the CB and receptacle would be easy.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
infinity said:
Look at 210.21(B)(1).
Trevor I think Table 210.21(B)(3) clearly states that a 15 amp circuit cannot have a 20 amp receptacle. Article 210.21 (B)(1) IMO means you cannot have less than that of the branch circuit. It does not say you can have more-- "not less than" would imply you could have more, however Table 210.21(B)(3) nullifies that statement.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The reason you can't place a 20a receptacle on a 15a circuit is that the slot shape of a 20a receptacle implies that the circuit is capable of supplying equipment that comes equipped a 20a plug, meaning that a 15a circuit is not capable of supplying the power the equipment with the 20a plug requires.

Whew!


Cavie said:
20A circuit can have 15 amp recp. go figure.
Unless it's a single-receptacle circuit.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
LarryFine said:
The reason you can't place a 20a receptacle on a 15a circuit is that the slot shape of a 20a receptacle implies that the circuit is capable of supplying equipment that comes equipped a 20a plug, meaning that a 15a circuit is not capable of supplying the power the equipment with the 20a plug requires.

Whew!



Unless it's a single-receptacle circuit.

There is no problem if we have a 15 amp receptacle on a 20 amp breaker because nothing requiring 20 amps will plug into it.But we could put a 20 amp load on a 15 amp breaker if we permit that 20 amp receptacle.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Dennis,
Trevor I think Table 210.21(B)(3) clearly states that a 15 amp circuit cannot have a 20 amp receptacle. Article 210.21 (B)(1) IMO means you cannot have less than that of the branch circuit. It does not say you can have more-- "not less than" would imply you could have more, however Table 210.21(B)(3) nullifies that statement.
210.21(B)(3) has no effect on 210.21(B)(1) as (B)(3) only applies to a branch circuit supplying two or more receptacles or outlets, while (B)(1) applies to a single receptacle installed on an individual branch circuit. Please note that a duplex receptacle is two receptacles.
Don
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
don_resqcapt19 said:
Dennis,

210.21(B)(3) has no effect on 210.21(B)(1) as (B)(3) only applies to a branch circuit supplying two or more receptacles or outlets, while (B)(1) applies to a single receptacle installed on an individual branch circuit. Please note that a duplex receptacle is two receptacles.
Don
Again I stand corrected...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
don_resqcapt19 said:
Dennis,

210.21(B)(3) has no effect on 210.21(B)(1) as (B)(3) only applies to a branch circuit supplying two or more receptacles or outlets, while (B)(1) applies to a single receptacle installed on an individual branch circuit. Please note that a duplex receptacle is two receptacles.
Don


That was my point, table 210.21(B)(3) is not for a single receptacle. A single receptacle is permitted to be rated larger than the circuit ampacity. So a 20 amp single receptacle is permitted on a 15 amp circuit.
 