    I have come across a set up where 100 amp service terminates to a 125 amp panel. The larger panel seems to be used to accomodate more breakers which power the large amount of lights and outlets in the home. However there are only 60 amps out of the 100 being used.
    Does this config need to be changed? If so why and how?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    16,800
    Re: 100 amp service to a 125 amp panel
    Are you saying the service entrance conductors are terminated to a 125 amp OCPD, or is there a 100 amp OCPD installed in a 125 amp rated panel?
    Roger
    Join Date
    May 2004
    Posts
    4
    A 125 amp rated panel with a 100 amp OCPD as the main and a sub with a 20 or more breakers.
    My apolgies for mixing terminology. Keep me straight.....I'm learning.
  4. #4
    Join Date
    Dec 2003
    TAMPA FLORIDA
    Posts
    4,576
    I see nothing wrong with that installation.Many times the panel is rated far higher than the main breaker,often to get more spaces.
    Tampa Florida
  5. #5
    Join Date
    May 2004
    Posts
    4
    I again got negative comments about this set up from a pesky inspector.
    Thanks for the reply.
  6. #6
    Join Date
    Dec 2003
    TAMPA FLORIDA
    Posts
    4,576
    Solve them problems in 2 ways.First carry a copy of 2002 nec and second ask him to find the violation in the code book.While he is looking go take lunch.
    Tampa Florida
  7. #7
    Join Date
    Feb 2003
    Fl
    Posts
    16,800
    Ask the inspector to explain how you can provide 50 amp fuses for a piece of equipment if you can't provide a fusible switch rated at 60 amps?
    This is the same thing.
    Roger
    Join Date
    Feb 2003
    Posts
    1,029
    What does this mean?
    Bill
  9. #9
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    I imagine he means that the total demand load is at 60-amperes on the 100-ampere service.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  10. #10
    Join Date
    Oct 2003
    Southern California
    Posts
    2,010
    I'm one inspector who thinks it's ok.
    What were his negative comments?
    I hope things work out in your favor.
    I'm a Retired Inspector, what do I know?