A friend sent me an email asking why a dp breaker rated 120/277 cannot be used for 240 Volts. I have never noticed a breaker rated that way. Any help.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
My first though would be to refer him to the "eyeglasses at Wal-Mart" thread :)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A friend sent me an email asking why a dp breaker rated 120/277 cannot be used for 240 Volts. I have never noticed a breaker rated that way. Any help.
If it was actually marked that way, there is no reason why you can't use it on a 120/240 volt system. The first number is the maximum permitted voltage to ground and the second is the maximum permitted phase to phase voltage. You could not use it on a 3 wire 240 volt system because of the 120 volt part of the "slash" rating.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Well thanks for the replys but apparently he was talking about a DP switch not a CB. I guess I never look at them -- they are rated 120/277. I told him exactly what Don said. Thanks again and sorry for the confusion-- I should know better than to post for someone without all the info.
 