    Is a laundry circuit considered an individual branch circuit?? and if so is it required by code to have a single receptacle outlet?? Is a washer considered a utilization equipment? In the hand book it states: An individual branch circuit, which supplies only one utilization equipment Via a single receptacle. What does via mean??
  2. #2
    Join Date
    Apr 2003
    Planet macmikeman
    Posts
    3,443
    Re: laundry branch circuit
    You are permitted to have more than one receptacle outlet on the laundry circuit. You are not allowed to take this circuit out of the laundry area to serve other loads.
    85deg. an Sunny today.
  3. #3
    Join Date
    Jan 2005
    Posts
    3,034
    And if it is a dedicated receptacle and wired in #12 than either a single round 20 a recp. or a 20 amp duplex
  4. #4
    Join Date
    Mar 2004
    Arizona
    Posts
    3,913
    VIA ; by means of
    frank
    Frank Arizona,USA
  5. #5
    Join Date
    Dec 2003
    TAMPA FLORIDA
    Posts
    4,576
    Watch out on this one.If this washer is there on final make sure the paper work isn't.It might call for a dedicated circuit.
    Tampa Florida
  6. #6
    Join Date
    Jan 2004
    Right here.
    Posts
    12,326
    That sounds like advice from a guy that's been there! Uh-huh... I got dinged on that once too. You could have knocked me over with a feather.
  7. #7
    Join Date
    Feb 2003
    Boston, MA
    Posts
    6,870
    Or a 15 amp duplex.
    There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan
    Open shop since 1988
  8. #8
    Join Date
    Dec 2004
    North Carolina
    Posts
    4,483
    Let me see if I can get something started here about this laundry receptacle.
    In 210.11 (C) (2) it states “to supply the laundry receptacle outlet(s) required by 210.52(F).”
    The reason for the letter (S) after the word outlet is to allow a gas dryer to be plugged in this same receptacle.
    Mike Whitt
    God answers Knee-Mail.
  9. #9
    Join Date
    Apr 2003
    Planet macmikeman
    Posts
    3,443
    JWelectric, if thats the case then I did a big oops as recently as yesterday because I ran a second outlet in the laundry on the adjacent wall in the same room to be used for say "a radio" or say "one of those lovely little smell devices I see on tv" but certainly not an "iron" which might get used at the same time as the washer.
  10. #10
    Join Date
    Dec 2004
    North Carolina
    Posts
    4,483
    macmikeman
    I have a couple of receptacles in my laundry room that are on the same circuit as the washer. While the washer is doing a load I will sometimes knock the wrinkles out of a shirt that was left in the dryer from the last load.
    Most of the time when I do this I will listen to a little of Floyd’s Another Brick in the Wall.
    It gets a little warm in our laundry so I will also have a small box fan blowing at the same time.
    This don’t change the fact that “outlet(s)” was left in the section to allow for a gas dryer to have a place to be plugged in.