Concerning formula manipulation and interpreting results:



When I get 370 A as the result of dividing 250 kVA by (390 V x 1.73), is that the current that I should expect to measure on each individual phase conductor? :-?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
a 3 phase 250 kva generator with a 390 volt output would be 370 amps per phase. 390 volt ??? where
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When I get 370 A as the result of dividing 250 kVA by (390 V x 1.73), is that the current that I should expect to measure on each individual phase conductor? :-?
While we don't say current "per phase," 370a from a supply is the same thing as 370a "per phase."

A given current on one conductor is that much current. We get more power at a given current by having a higher voltage, more phases, or both.

Remember that current is a function of voltage and impedance. The voltage is a constant; the current varies inversely with the impedance.
 