Combined units ~ # of services

Status
Not open for further replies.

celtic

Senior Member
Location
NJ
I have a situation where a HO bought a condo unit adjacent to the one he resides in. His plan is to demo a demising wall and have one huge condo.

My question is in regards to the service/s.
Both units are seperately metered (150 or 175 A each).
Under 230.2(B)(1) and 230.4(E) would the present arrangement be allowed?
I understand the AHJ's input may be required (special written permission), but at this point I'm just looking for any opinions and/or Articles.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Cant speak for condos, but we did a 2-to-1 townhouse job recently, and we had to rearrange the service so it was a single 400 amp instead of 2-200. I didn't work there until the final stage, but I'll ask about it monday.
 

jtester

Senior Member
Location
Las Cruces N.M.
Just because you have separate meters doesn't mean you have separate services. I regularly encounter that in commercial, and never hesitated to feed one space with two meters, until the local utility said they wouldn't permit it any longer.

Jim T
 

JohnJ0906

Senior Member
Location
Baltimore, MD
I just recalled the reason the service had to be redone in the job I mentioned-Grouping of disconnects. Celtic, I think you will have to check with AHJ and POCO on this one
 

celtic

Senior Member
Location
NJ
JohnJ0906 said:
I just recalled the reason the service had to be redone in the job I mentioned-Grouping of disconnects. Celtic, I think you will have to check with AHJ and POCO on this one

The disco comes from a meter bank room with 68 +/- meters/disco...feed from 1200/800 MDP's. I don't know that both units come from the same MDP...have to check.
 