Closed Thread
Results 1 to 8 of 8
Thread: Exit Sign Mounting Height?
  1. #1
    Join Date
    Sep 2003
    Posts
    117
    Is there any provision for "Exit Sign" mounting height? I have looked up NFPA 101 and NEC, but I wasn't lucky enough to find it. Can anyone help me? Thanks in advance.
    [ November 07, 2003, 04:44 PM: Message edited by: jkim780 ]
  2. #2
    Join Date
    May 2003
    Salt Lake City, Utah
    Posts
    5,319
    Re: Exit Sign Mounting Height?
    I don't see anything in the IBC or ANSI A117.1 either. I am not aware of any provisions that govern it.
    Ryan Jackson, Salt Lake City
    Inspector, Instructor
  3. #3
    Join Date
    Sep 2003
    Posts
    117
    Ryan,
    What does that mean, then? That means that we can mount exit sign any height we want as long as readily visible? Even 12' A.F.F.?
    Can we apply this exit sign to Visual alarm signal appliances(A117.1/NFPA)which is 80"mim,96"max A.F.F.?
  4. #4
    Join Date
    May 2003
    Posts
    5,319
    I don't what to tell you, but I think it would be a bit of a stretch to call an exit sign a visual or audible alarm. If you are looking at the ANSI, take a look at table 703.4.2.4. It doesn't address exit signs per sa, but signs located between 10' to 21'could be compliant with accessibility provisions.
    :confused:
  5. #5
    Join Date
    Sep 2003
    Posts
    117
    :confused:
    Ryan, What is accessiblitity provisions?
  6. #6
    Join Date
    May 2003
    Posts
    5,319
    When used in context with a building code or the ANSI, accessible means that it is usable to people with disabilities.
    In the above example, I bring it up because accessibility provisions are much more stringent that other requirements. Example: The nec doesn't care at what elevation you install a general use snap switch. The ANSI A117.1 does care and will not allow you to install more than 48" AFF. That is an accessibility provision.
  7. #7
    Join Date
    Feb 2003
    Cleveland, Ohio
    Posts
    1,321
    With the exception of California, there isn't any height maximum in terms of a measurement.
    2002 NFPA 101 Life Safety Code
    7.10.1.7* Visibility.
    Every sign required in Section 7.10 shall be located and of such size, distinctive color, and design that it is readily visible and shall provide contrast with decorations, interior finish, or other signs. No decorations, furnishings, or equipment that impairs visibility of a sign shall be permitted. No brightly illuminated sign (for other than exit purposes), display, or object in or near the line of vision of the required exit sign that could detract attention from the exit sign shall be permitted.
  8. #8
    Join Date
    May 2003
    MA
    Posts
    409
    I just dealt with this on a project and I know the the minimum head room for a means of egress I believe is either 7' or 7'-6". Therefore the bottom of the exit sign should be at least above that height.
Closed Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts