receptacle location

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
I know that a flexible is not allowed to be installed above a ceiling space but what about a receptacle? A local inspector told me that recepacles are not allowed to be installed above a ceiling. Is this true I was searching the NEC but could not find the statement that either allowed a receptacle above a ceiling or did not allow this any thoughts. two additional questions is there a site that would inform me what edition of the code a certian state has adopted? and last but not least what are some thoughts on ac hipot testing utilizing a tan-delta system? I have read that a dc hipot can damage insulation but the ac hipot tan-delta that measures phase angles does not is this true? what are the advantages / disadvantages of either type of testing. thanks in advance for your help / thoughts.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
As for the outlet above the ceiling. Yes you may install an outlet above the ceiling. No you may not plug anything into it that is not attended. 400.8(5)
 