2008 517.18 (B) Patient Bed Location Receptacles. Each patient bed
location shall be provided with a minimum of four receptacles.
They shall be permitted to be of the single or duplex
types or a combination of both. All receptacles, whether
four or more, shall be listed ?hospital grade? and so identified.
The grounding terminal of each receptacle shall be
connected to an insulated copper equipment grounding conductor
sized in accordance with Table 250.122
 