Circuiting question during design. I have multiple VAV boxes that are 277/1 with only heat, no motor, same load. My plan is to group a bunch of them and homerun them back to the panel with a 60A/3P 480/V circuit.
My question is how would the guys out in the field alternate these loads? My belief is the guys would treat this as a load balance issue. Basically carry 3-phase through-out the circuit and alternate equipment on phases. Please let me know what you think.