Can NMC be used above a lay in ceiling in an assisted care living facility?
M MF54 Member Dec 12, 2006 #1 Can NMC be used above a lay in ceiling in an assisted care living facility?
raider1 Senior Member Staff member Location Logan, Utah Dec 12, 2006 #2 No, take a look at 334.12(A)(2) Chris
D dcspector Senior Member Location Burke, Virginia Dec 12, 2006 #3 Per NEC 334.12(A)(2) I would say no....Also, IBC does not classify Assisted living under multi family or one and two family which would be permissible.
Per NEC 334.12(A)(2) I would say no....Also, IBC does not classify Assisted living under multi family or one and two family which would be permissible.
D dcspector Senior Member Location Burke, Virginia Dec 12, 2006 #4 Sorry Chris I posted about same time.......
raider1 Senior Member Staff member Location Logan, Utah Dec 12, 2006 #5 Sorry Chris I posted about same time....... Click to expand... Not a problem, I do the same thing all the time. Chris
Sorry Chris I posted about same time....... Click to expand... Not a problem, I do the same thing all the time. Chris