rhombus65 said:The NEC says that if you run romex above a commercial drop ceiling the romex must be secured to framing and not stung across the ceiling.
rhombus65 said:Is there a mass amendment that voids this requirement?
334.12(1). Revise to read as follows:
In dropped or suspended ceilings in other than
one- and two-family and multifamily dwellings,
unless run so as to closely follow the surface of
framing members, running boards, or the
equivalent, or unless connected to luminaires
(lighting fixtures) in accordance with
334.30(B)(2).
Jim W in Tampa said:Starting to wonder about Ma.,seems anything they don't want to do or like they just change .
90.4. Revise the first paragraph to read as follows:
90.4 Enforcement. This Code shall be used by the
authority enforcing the Code and exercising legal
jurisdiction over electrical installations. The authority
having jurisdiction of enforcement of the Code
shall accept listed and labeled equipment or materials
where used or installed in accordance with instructions
included with the listing or labeling. The
authority shall have the responsibility for deciding
upon the approval of unlisted or unlabeled equipment
and materials, and for granting the special
permission contemplated in a number of the rules.
Jim W in Tampa said:Starting to wonder about Ma.,seems anything they dont want to do or like they just change .