Old 10-28-2005, 10:36 AM
maryl maryl is offline
Junior Member
Default Lock out/Tag out
I need an answer quickly! A Contractor & Subcontractor Safety Manual thatI just received contains a LOTO policy stating that their Maintenance Dept. will apply, and be responsibile for the removal of their lock and tag when one of our employees needs to work on de-energized equipment. I say "NO! NO! NO!" Can anyone give me a reference to NEC, NFPA 70E, or other, that specifically states that the person who is actually working on the equipment is the one with sole responsibility to perform the LOTO or at least apply their personal lock with the Maintenance Dept.'s.
OSHA uses the term "Authorized person".
  #2
Old 10-28-2005, 11:13 AM
petersonra petersonra is online now
Default Re: Lock out/Tag out
it is not unusual for the plant to apply a lock in such a situation. in most cases the individuals doing the work would also apply a lock.
if the number of people working on the locked out device makes that impractical, you can do something else.
this is not a NEC issue though.
[ October 28, 2005, 11:14 AM: Message edited by: petersonra ]
__________________
Bob
  #3
Old 10-28-2005, 11:15 AM
don_resqcapt19's Avatar
don_resqcapt19 don_resqcapt19 is offline
Does it say that the worker cannot place his own lock in addition to the "owners" lock? In many industrial applications, the plant people must place the first lock to prevent problems with accidental shutdown of their processes, but the work must also place his personal lock.
Don
__________________
Don, Illinois
"It is the first responsibility of every citizen to question authority." B Franklin
  #4
Old 10-28-2005, 11:19 AM
bphgravity bphgravity is offline
I believe the NFPA 70E (section 120) places the responsibility of the LOTO procedure to be established by the employer. I don't believe there is a specific requirement that only the person performing the work install and/or remove the device.
I also don't believe OSHA (1926.146) madates this either.
I definetly feel this is a good work practice and should be employed into the LOTO procedures, however, if the company has a documented and established procedure otherwise, I think it is compliant with minimum safety requirements.
__________________
Bryan P. Holland, ICC Electrical Code Official
CBO, Plans Examiner, Inspector, Instructor
Secretary - IAEI Florida Gulf Coast Division
Secretary - BOAF Gulf Coast Chapter
  #5
Old 10-28-2005, 11:54 AM
charlie b's Avatar
charlie b charlie b is offline
I would want the LOTO procedure to clearly state the actions that the maintenance department personnel must take, to verify the work is complete and the area is clear, before they are permitted to remove the tag. I would insert a step requiring the signature of the worker as a prerequisite for removing the tag.
__________________
Charles E. Beck, P.E., Seattle
  #6
Old 10-28-2005, 12:36 PM
Junior Member
Thanks for all your timely help. I will instruct our empolyees that they also need to attach their lock in addition to the customer's. It makes sence that the customer would want to be the ones to de-energize and LO seeing they know their machinery better than we would.
Again, thanks.
  #7
Old 10-28-2005, 01:06 PM
From an OSHA letter ruling.
[quote]Question 2:
Does an on-site agency, such as an utility, have the right to restrict or limit the use of lockout/tagout procedures at their facility to only one procedure, specifically their own, when multiple contractors with individual procedures are involved?
Reply:
Lockout/Tagout procedures used by outside personnel (contractors, etc.) are covered by 1910.147(f)(2). This standard requires on-site employers and outside employers to inform each other of their respective lockout/tagout procedures. Furthermore, an on-site employer is required to ensure that his personnel understand and comply with restrictions and prohibitions of the outside employer's energy control procedures. Outside employers are not required to use on-site employer lockout/tagout procedures.[quote]
__________________
Don, Illinois
  #8
Old 10-28-2005, 02:58 PM
however, if you choose not to follow thier policy they could decide to get another contractor.
it seems to me that we rely way too much on what some government rule says rather than just talking to each other and working out a solution that is acceptable to all concerned.
__________________
Bob
  #9
Old 10-28-2005, 04:11 PM
Bob,
My point is that they can't stop you from putting your own lock on while you are working on the equipment, and if they wouldn't let me do that, they would be looking for another contractor, because I won't let any of my guys work without having their own lock on the equipment.
Don
__________________
Don, Illinois
  #10
Old 10-28-2005, 04:21 PM
sparky_magoo's Avatar
sparky_magoo sparky_magoo is offline
I carry my own lock. I used it today at a sewage treatment facility. The city facility guys also put their own lock on. If they would have told me I can't put my oen lock on, I would have walked away. I'm sure my boss would have backed me up.
__________________
"I'm impatient with stupidity. My people have learned to live without it." Quote: Klaatu
Closed Thread
CEU Banner Home Page
Search this Thread:
Advanced Search
Display Modes