200amp service...2 ground rods spaced six ft apart # 6 wire from rod to rod then to meter....#4 to water main...is something missing??????????????
state is massachusetts
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
so far see no problem. are there any other electrodes present ? (CEE, building steel, etc.) any metal piping that needs bonding ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
250.24 allows you to connect your grounding electrode conductor at any point from service drop (or lateral) to the 1st disconnecting means. If POCO has no problem the connection can be made at the meter. All grounding electrode conductors do not need to come form the same place, so the GEC to the rods can come from the meter, the GEC to water from the panel.
The GEC could come from the rod to the water but it would need to be #4 to each (no weak link).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
250.24 allows you to connect your grounding electrode conductor at any point from service drop (or lateral) to the 1st disconnecting means. If POCO has no problem the connection can be made at the meter. All grounding electrode conductors do not need to come form the same place, so the GEC to the rods can come from the meter, the GEC to water from the panel.
The GEC could come from the rod to the water but it would need to be #4 to each (no weak link).


Here's a graphic to go along with Augie's post: