    receptacle outlets at stair landings

    Am I wrong but doesn't stairs count as wall space and a receptacle outlet would be required at the landing??

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,388
    Not to my knowledge. Do you have a code article in mind to back up your thought?
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  3. #3
    Join Date
    Nov 2003
    Location
    Lancaster,Pa
    Posts
    212
    You cannot put anything there to plug in because you don't want anything in your way when you are about to burn up. I'm sure since the NEC is part of the fire code,they would not have us put a recept in a stairwell or landing.
    Action Jackson (A.J.)

  4. #4
    Join Date
    Mar 2006
    Location
    Tampa Florida
    Posts
    8,009
    Its not a habitable room so no receptacle required.However nothing stops you from putting one in

  5. #5
    Join Date
    Mar 2006
    Posts
    23
    In the IRC (E3801.2.1) it defines wall space as railing or wall space on the other side

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,388
    Quote Originally Posted by insparks
    In the IRC (E3801.2.1) it defines wall space as railing or wall space on the other side

    Not all wall space automatically require receptacles. One example would be a hallway of less than 10 feet. It has lots of wall space but doesn't require any receptacles. Also a stairway landing doesn't fall under the general provision requirements of 210.52(A)
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  7. #7
    Join Date
    Feb 2003
    Location
    Boston, MA
    Posts
    6,856

    Re: receptacle outlets at stair landings

    Quote Originally Posted by insparks
    Am I wrong but doesn't stairs count as wall space and a receptacle outlet would be required at the landing??
    Using this logic you would also need receptacles on the wall space along the stairway itself.
    Not required but not prohibited.
    On some larger landings not a bad idea.
    There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan

    Open shop since 1988

  8. #8
    Join Date
    Mar 2006
    Location
    Northwest
    Posts
    34
    This landing could be considered a hallway 10 ft rule; however, the print should determine this specifically... ie loft landing hallway use common sense and chose your battles wisely with the inspectors.