Bonding bushings 1 1/4"

Status
Not open for further replies.

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Bonding bushings have no correlation to conduit size. You either need them or you don't, conduit size isn't a factor.
 

K2500

Senior Member
Location
Texas
The bushing requirement was for conduit containing wire #4 and larger, rather than by conduit size. 300.4(g)
Also depends on raceway type and fittings 344.46, 342.46.
 
Last edited:
Thanks for the help guys I couldn't find a reference but I could have sworn it was in there.
But at my age it could have been decades ago
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
For years I was told that 1" conduit requied a bushing, but then I realized that was someone had heard wrong and that was probably the size you need to run #4 in.
 

NolaTigaBait

Senior Member
Location
New Orleans,LA
For years I was told that 1" conduit requied a bushing, but then I realized that was someone had heard wrong and that was probably the size you need to run #4 in.

I was told that also...My old boss said anything over 3/4 required a bushing....He also told me it was ok to tap a branch circuit down one size up to 12''....He called it the 12 '' tap rule....Needless to say neithert of them are in the code book, but I did it like this until I actually read it.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I was told that also...My old boss said anything over 3/4 required a bushing....He also told me it was ok to tap a branch circuit down one size up to 12''....He called it the 12 '' tap rule....Needless to say neithert of them are in the code book, but I did it like this until I actually read it.

I had to look to see where you were from to get your name. It just really caught my eye, because my mom's name is Nola.:)
 