    Can anyone find an NEC reference that when wiring is surfaced mounted (exposed wiring, i.e., romex) it shall be protected to height of seven feet from floor level.
    I'm not sure if this is an OSHA requirement or NEC.
  2. #2
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,201
    You might be thinking about 300.5(D)(1) that says direct buried conductors emerging from grade shall be protected by a raceway or enclosure from the minimum cover distance to a point at least 8 feet above finished grade. Also take a lok at 334.15(B) for protection of NM cable.
    Chris
  3. #3
    Join Date
    Mar 2006
    Ohio
    Posts
    1,758
    Re: Romex physical protection
    NEC 334.15(B) "Cable shall be protected from physical damage where necessary"
    NEC 90.4 "The authority having jurisdiction for enforcement of the Code has the responsibility for making interpretations of the rules"
    There is no 7 foot measurement nor is there uniform agreement, from one jurisdiction to the next, on what areas are subject to physical damage. Ask your local inspector what their policy is
    David
  4. #4
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    Someone was probably referencing 320.23(A) when installing NM cables in an accessible attic.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  5. #5
    Join Date
    Oct 2004
    Oregon
    Posts
    115
    There may be local amendments to the NEC, such as this one in Oregon:
    (3) Amend Section 334.15(B) Protection from Physical Damage by adding: "Exposed nonmetallic sheathed cable shall be protected where it is installed horizontally below 8 feet above the floor. Exposed nonmetallic sheathed cable below 8 feet above the floor that enters the top or bottom of a panelboard shall be protected from physical damage by conduit, raceway, 1/2" plywood or 1/2" drywall."
    -- Steve
  6. #6
    Join Date
    Apr 2006
    Posts
    2
    NEC 230.50
    Thanks everyone. I also found related information in 230.50.
  7. #7
    Join Date
    Feb 2005
    NJ
    Posts
    9,328
    Re: NEC 230.50
    Quote Originally Posted by rltramble
    I don't see how...230 is services...
    .. 334.12(A)3 et al
    Is this apples and oranges?
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    CELTIC
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    An error on your part does not constitute an emergency on my part.8-)